Hello,
You are seeing the effects of the thermal radiant exchange with a sky
that is colder than the surfaces. To see the effects that you want
to see all you have to do is set the line
".9, !- Absorptance:Thermal" to a
very small value ie. 0.001 . This will effectively make the
surfaces made with this concrete material low-e surfaces.
Add these report variables lines to your current input file and you will
see how the roof exterior temp is ~15C. This of course with the
effects from the walls drops the interior temp the ~4C that you are
experiencing. Then change the line in the material as shown above
and the temperatures will be what you were expecting.
Report Variable,*,Surface Inside Temperature,hourly;
Report Variable,*,Surface Outside Temperature,hourly;
You are attempting to run cases to give yourself confidence in the
algorithms and it is always interesting to find that we forget things
that the program remembers.
MATERIAL:REGULAR,
concreteWall, !- Name
MediumSmooth, !- Roughness
.3, !- Thickness {m}
1.7, !- Conductivity {W/m-K}
2240, !- Density {kg/m3}
836, !- Specific Heat {J/kg-K}
.9, !- Absorptance:Thermal
.7, !- Absorptance:Solar
.7; !- Absorptance:Visible
Richard L.
Thanks
Dr. Richard J. Liesen Ph.D. M.E.
Associate Director, Building Systems Laboratory
Department of Mechanical and Industrial Engineering
University of Illinois at Urbana-Champaign
At 11:35 AM 6/4/2002, cdharrisie2002 wrote:
Hi,
I am currently evaluating EnergyPlus as we hope to use it for
simulating the energy performance of a proposed new hospital building
in Dublin, Ireland. I have currently modelled a very simple concrete
cube for 2 design days, which have constant outdoor temperature. The
simulated inside zone temperature for both days is also constant but
about 4.5 degrees higher than the outdoor temperature. I expected the
temperatures to be the same, as there is no heat input to the
building. Is there a reason for the higher inside temperature or have
i modelled the building incorrectly?
Thank you in advance for your help.
Best regards
Colin Harris
Trinity College Dublin.
THE IDF FILE BELOW :-
!-Generator IDFEditor 1.05
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are
generated automatically.
!- Use '!' comments if they need to be
retained when using the
IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION
===========
VERSION,
1.0.1;
!- Version Identifier
!- =========== ALL OBJECTS IN CLASS: BUILDING
===========
BUILDING,
hospital,
!- Building Name
0,
!- North Axis {deg}
Country,
!- Terrain
.04,
!- Loads Convergence Tolerance Value {W}
.004,
!- Temperature Convergence Tolerance
Value {C}
MinimalShadowing; !- Solar
Distribution
!- =========== ALL OBJECTS IN CLASS: TIMESTEP IN HOUR
===========
TIMESTEP IN HOUR,
4;
!- Time Step in Hour
!- =========== ALL OBJECTS IN CLASS: INSIDE CONVECTION
ALGORITHM
===========
INSIDE CONVECTION ALGORITHM,
Detailed;
!- InsideConvectionValue
!- =========== ALL OBJECTS IN CLASS: OUTSIDE CONVECTION
ALGORITHM
===========
OUTSIDE CONVECTION ALGORITHM,
Detailed;
!- OutsideConvectionValue
!- =========== ALL OBJECTS IN CLASS: SKY RADIANCE
DISTRIBUTION
===========
SKY RADIANCE DISTRIBUTION,
1;
!- SkyRadianceValue
!- =========== ALL OBJECTS IN CLASS: SOLUTION ALGORITHM
===========
SOLUTION ALGORITHM,
CTF;
!- SolutionAlgo
!- =========== ALL OBJECTS IN CLASS: SHADOWING
CALCULATIONS
===========
SHADOWING CALCULATIONS,
20;
!- Period_for_calculations
!- =========== ALL OBJECTS IN CLASS: ZONE VOLUME
CAPACITANCE
MULTIPLIER ===========
ZONE VOLUME CAPACITANCE MULTIPLIER,
1;
!- Capacitance Multiplier
!- =========== ALL OBJECTS IN CLASS: RUN CONTROL
===========
RUN CONTROL,
No,
!- Do the zone sizing calculation
No,
!- Do the system sizing calculation
No,
!- Do the plant sizing calculation
Yes,
!- Do the design day simulations
No;
!- Do the weather file simulation
!- =========== ALL OBJECTS IN CLASS: LOCATION
===========
Location,
Dublin,
!- LocationName
53.43,
!- Latitude {deg}
-6.25,
!- Longitude {deg}
0,
!- TimeZone {hr (decimal)}
85;
!- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: DESIGNDAY
===========
DesignDay,
SummerDayDUB-IRL, !-
DesignDayName
24.2,
!- Maximum Dry-Bulb Temperature {C}
0,
!- Daily Temperature Range {C}
17.2,
!- Wet-Bulb Temperature At MaxTemp {C}
99433,
!- Barometric Pressure {Pa}
0,
!- Wind Speed {m/s}
221,
!- Wind Direction {deg}
0,
!- Sky Clearness
0,
!- Rain Indicator
0,
!- Snow Indicator
27,
!- Day Of Month
7,
!- Month
Friday,
!- Day Type
0;
!- Daylight Saving Time Indicator
DesignDay,
WinterDayDUB-IRL, !-
DesignDayName
2,
!- Maximum Dry-Bulb Temperature {C}
0,
!- Daily Temperature Range {C}
0,
!- Wet-Bulb Temperature At MaxTemp {C}
99433,
!- Barometric Pressure {Pa}
0,
!- Wind Speed {m/s}
221,
!- Wind Direction {deg}
0,
!- Sky Clearness
0,
!- Rain Indicator
0,
!- Snow Indicator
20,
!- Day Of Month
1,
!- Month
Friday,
!- Day Type
0;
!- Daylight Saving Time Indicator
!- =========== ALL OBJECTS IN CLASS: MATERIAL:REGULAR
===========
MATERIAL:REGULAR,
concreteWall,
!- Name
MediumSmooth,
!- Roughness
.3,
!- Thickness {m}
1.7,
!- Conductivity {W/m-K}
2240,
!- Density {kg/m3}
836,
!- Specific Heat {J/kg-K}
.9,
!- Absorptance:Thermal
.7,
!- Absorptance:Solar
.7;
!- Absorptance:Visible
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION
===========
CONSTRUCTION,
wall,
!- Name
concreteWall;
!- Outside Layer
!- =========== ALL OBJECTS IN CLASS: ZONE
===========
ZONE,
cube,
!- Zone Name
0,
!- Relative North (to building) {deg}
0,
!- X Origin {m}
0,
!- Y Origin {m}
0,
!- Z Origin {m}
1,
!- Type
1,
!- Multiplier
20,
!- Ceiling Height {m}
70000;
!- Volume {m3}
!- =========== ALL OBJECTS IN CLASS: SURFACEGEOMETRY
===========
SurfaceGeometry,
UpperLeftCorner, !-
SurfaceStartingPosition
CounterClockWise, !-
VertexEntry
relative;
!- SurfaceGeometryKey
!- =========== ALL OBJECTS IN CLASS:
SURFACE:HEATTRANSFER
===========
Surface:HeatTransfer,
southWall,
!- User Supplied Surface Name
WALL,
!- Surface Type
wall,
!- Construction Name of the Surface
cube,
!- InsideFaceEnvironment
ExteriorEnvironment, !-
OutsideFaceEnvironment
,
!- OutsideFaceEnvironment Object
SunExposed,
!- Sun Exposure
WindExposed,
!- Wind Exposure
.5,
!- View Factor to Ground
4,
!- Number of Surface Vertice Groups --
Number of (X,Y,Z) groups in this surface
0,
!- Vertex 1 X-coordinate {m}
0,
!- Vertex 1 Y-coordinate {m}
20,
!- Vertex 1 Z-coordinate {m}
0,
!- Vertex 2 X-coordinate {m}
0,
!- Vertex 2 Y-coordinate {m}
0,
!- Vertex 2 Z-coordinate {m}
50,
!- Vertex 3 X-coordinate {m}
0,
!- Vertex 3 Y-coordinate {m}
0,
!- Vertex 3 Z-coordinate {m}
50,
!- Vertex 4 X-coordinate {m}
0,
!- Vertex 4 Y-coordinate {m}
20;
!- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
eastWall,
!- User Supplied Surface Name
WALL,
!- Surface Type
wall,
!- Construction Name of the Surface
cube,
!- InsideFaceEnvironment
ExteriorEnvironment, !-
OutsideFaceEnvironment
,
!- OutsideFaceEnvironment Object
SunExposed,
!- Sun Exposure
WindExposed,
!- Wind Exposure
.5,
!- View Factor to Ground
4,
!- Number of Surface Vertice Groups --
Number of (X,Y,Z) groups in this surface
50,
!- Vertex 1 X-coordinate {m}
0,
!- Vertex 1 Y-coordinate {m}
20,
!- Vertex 1 Z-coordinate {m}
50,
!- Vertex 2 X-coordinate {m}
0,
!- Vertex 2 Y-coordinate {m}
0,
!- Vertex 2 Z-coordinate {m}
50,
!- Vertex 3 X-coordinate {m}
70,
!- Vertex 3 Y-coordinate {m}
0,
!- Vertex 3 Z-coordinate {m}
50,
!- Vertex 4 X-coordinate {m}
70,
!- Vertex 4 Y-coordinate {m}
20;
!- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
roof,
!- User Supplied Surface Name
ROOF,
!- Surface Type
wall,
!- Construction Name of the Surface
cube,
!- InsideFaceEnvironment
ExteriorEnvironment, !-
OutsideFaceEnvironment
,
!- OutsideFaceEnvironment Object
SunExposed,
!- Sun Exposure
WindExposed,
!- Wind Exposure
0,
!- View Factor to Ground
4,
!- Number of Surface Vertice Groups --
Number of (X,Y,Z) groups in this surface
0,
!- Vertex 1 X-coordinate {m}
0,
!- Vertex 1 Y-coordinate {m}
20,
!- Vertex 1 Z-coordinate {m}
50,
!- Vertex 2 X-coordinate {m}
0,
!- Vertex 2 Y-coordinate {m}
20,
!- Vertex 2 Z-coordinate {m}
50,
!- Vertex 3 X-coordinate {m}
70,
!- Vertex 3 Y-coordinate {m}
20,
!- Vertex 3 Z-coordinate {m}
0,
!- Vertex 4 X-coordinate {m}
70,
!- Vertex 4 Y-coordinate {m}
20;
!- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
northWall,
!- User Supplied Surface Name
WALL,
!- Surface Type
wall,
!- Construction Name of the Surface
cube,
!- InsideFaceEnvironment
ExteriorEnvironment, !-
OutsideFaceEnvironment
,
!- OutsideFaceEnvironment Object
SunExposed,
!- Sun Exposure
WindExposed,
!- Wind Exposure
.5,
!- View Factor to Ground
4,
!- Number of Surface Vertice Groups --
Number of (X,Y,Z) groups in this surface
50,
!- Vertex 1 X-coordinate {m}
70,
!- Vertex 1 Y-coordinate {m}
20,
!- Vertex 1 Z-coordinate {m}
50,
!- Vertex 2 X-coordinate {m}
70,
!- Vertex 2 Y-coordinate {m}
0,
!- Vertex 2 Z-coordinate {m}
0,
!- Vertex 3 X-coordinate {m}
70,
!- Vertex 3 Y-coordinate {m}
0,
!- Vertex 3 Z-coordinate {m}
0,
!- Vertex 4 X-coordinate {m}
70,
!- Vertex 4 Y-coordinate {m}
20;
!- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
westWall,
!- User Supplied Surface Name
WALL,
!- Surface Type
wall,
!- Construction Name of the Surface
cube,
!- InsideFaceEnvironment
ExteriorEnvironment, !-
OutsideFaceEnvironment
,
!- OutsideFaceEnvironment Object
SunExposed,
!- Sun Exposure
WindExposed,
!- Wind Exposure
.5,
!- View Factor to Ground
4,
!- Number of Surface Vertice Groups --
Number of (X,Y,Z) groups in this surface
0,
!- Vertex 1 X-coordinate {m}
70,
!- Vertex 1 Y-coordinate {m}
20,
!- Vertex 1 Z-coordinate {m}
0,
!- Vertex 2 X-coordinate {m}
70,
!- Vertex 2 Y-coordinate {m}
0,
!- Vertex 2 Z-coordinate {m}
0,
!- Vertex 3 X-coordinate {m}
0,
!- Vertex 3 Y-coordinate {m}
0,
!- Vertex 3 Z-coordinate {m}
0,
!- Vertex 4 X-coordinate {m}
0,
!- Vertex 4 Y-coordinate {m}
20;
!- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
floor,
!- User Supplied Surface Name
FLOOR,
!- Surface Type
wall,
!- Construction Name of the Surface
cube,
!- InsideFaceEnvironment
ExteriorEnvironment, !-
OutsideFaceEnvironment
,
!- OutsideFaceEnvironment Object
NoSun,
!- Sun Exposure
NoWind,
!- Wind Exposure
1,
!- View Factor to Ground
4,
!- Number of Surface Vertice Groups --
Number of (X,Y,Z) groups in this surface
50,
!- Vertex 1 X-coordinate {m}
0,
!- Vertex 1 Y-coordinate {m}
0,
!- Vertex 1 Z-coordinate {m}
0,
!- Vertex 2 X-coordinate {m}
0,
!- Vertex 2 Y-coordinate {m}
0,
!- Vertex 2 Z-coordinate {m}
0,
!- Vertex 3 X-coordinate {m}
70,
!- Vertex 3 Y-coordinate {m}
0,
!- Vertex 3 Z-coordinate {m}
50,
!- Vertex 4 X-coordinate {m}
70,
!- Vertex 4 Y-coordinate {m}
0;
!- Vertex 4 Z-coordinate {m}
!- =========== ALL OBJECTS IN CLASS: REPORT VARIABLE
===========
Report Variable,
*,
!- Key_Value
Outdoor Dry
Bulb, !- Variable_Name
hourly;
!- Reporting_Frequency
Report Variable,
*,
!- Key_Value
Zone/Sys Air Temp[C], !-
Variable_Name
hourly;
!- Reporting_Frequency
!- =========== ALL OBJECTS IN CLASS: REPORT
===========
Report,
Surfaces,
!- Type_of_Report
DXF;
!- Name_of_Report
Report,
Variable Dictionary; !-
Type_of_Report
Yahoo! Groups Sponsor
ADVERTISEMENT


To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to the
Yahoo! Terms of
Service.
| Yahoo! Groups Sponsor |
ADVERTISEMENT
![]() |
|
![]() |
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.