Re: [EnergyPlus_Support] Simple Steady State simulation
At 11:08 AM 6/5/2002, colin harris wrote:
The outdoor temperature is 24
degrees and indoor was around 19.5 degrees. I did what you suggested by
setting the absorptance to a low number and the inside temperature rose
to very near 24 degrees. I am now wondering what is the Sky temperature
phenomena, and how is this derived from the input data?
Thank you very much for your help. So far i have been very impressed with
EnergyPlus ease of installation and its comprehensive documentation and
now with the email group support.
Best regards
Colin.
Hello,
The sky temperature is calculated using the Sky Radiance Model in the
program. At night the sky looks like a cold black-body surface
which buildings exchange with radiantly. This is the answer to the
age old question of why puddles on the roof of a building can freeze when
the air temperature never drops below freezing. A description from
the Engineering Manual is included below which you can reference in more
detail.
Thanks Richard Liesen
Sky Radiance Model
- In EnergyPlus the calculation of diffuse solar radiation from the sky
incident on an exterior surface takes into account the anisotropic
radiance distribution of the sky. This calculation is done when the user
has chosen the anisotropic sky radiance option in BUILDING input
(SkyRadianceDistribution = 1). In this case the diffuse sky irradiance on
a surface is given by
- AnisoSkyMult(SurfNum) * DifSolarRad
- where DifSolarRad is the diffuse solar irradiance from the sky on the
ground and SurfNum is the number of the surface.
- AnisoSkyMult is determined by surface orientation and sky radiance
distribution, and accounts for the effects of shading of sky diffuse
radiation by shadowing surfaces such as overhangs. It does not account
for reflection of sky diffuse radiation from shadowing surfaces.
- The sky radiance distribution is based on an empirical model based on
radiance measurements of real skies, as described in Perez et al., 1990.
In this model the radiance of the sky is determined by three
distributions that are superimposed (see Figure 16)
- (1) An isotropic distribution that covers the entire sky
dome;
- (2) A circumsolar brightening centered at the position of the
sun;
- (3) A horizon brightening.
- The proportions of these distributions depend on the sky condition,
which is characterized by two quantities, clearness factor and
brightness factor, defined below, which are determined from sun
position and solar quantities from the weather file.
- The circumsolar brightening is assumed to be concentrated at a
point source at the center of the sun although this region actually
begins at the periphery of the solar disk and falls off in intensity with
increasing angular distance from the periphery.
- The horizon brightening is assumed to be a linear source at
the horizon and to be independent of azimuth. In actuality, for clear
skies, the horizon brightening is highest at the horizon and decreases in
intensity away from the horizon. For overcast skies the horizon
brightening has a negative value since for such skies the sky radiance
increases rather than decreases away from the horizon.
| Yahoo! Groups Sponsor |
ADVERTISEMENT
![]() |
|
![]() |
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.