Re: AW: [EnergyPlus_Support] Heat Exchanger



The WaterHeater:Simple object is a multipurpose object which can 
serve both domestic hot water demands and serve as a source of heat 
to a hot water coil loop.  It has a storage tank and can be heated by 
a burner or electric coil and/or it can be heated using recovered 
heat from a HEAT RECOVERY LOOP.  

The example file EnergyPlus\ExampleFiles\Misc\HRGenChill.idf uses 
waste heat from electric generators to provide some heat to the hot 
water coil loop.  It does not appear, though, that the right 
components are available to recover heat from the chiller condenser 
water loop.

Mike Witte





On 28 Jul 2002, at 18:18, Rainer Schubert wrote:

> The plan is to use a part of the condensate heat to heat water in a
> water storage tank or preheat water for the heating coil. And that?s the
> next question: what about a simple water storage tank?
>  
> Rainer
> -----Ursprüngliche Nachricht-----
> Von: Linda Lawrie [mailto:linda@xxxxxxxxxx] 
> Gesendet: Sunday, July 28, 2002 4:00 PM
> An: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Betreff: Re: [EnergyPlus_Support] Heat Exchanger
>  
> At 08:49 AM 7/28/02, Rainer Schubert wrote:
> 
> 
> I m looking for a heat exchanger water to water but can t find it in E+.
> Please tell me isn t there anyone in E+ or am I blind? :-)
> 
> There is heat pump: water to water both heating and cooling.  Is this
> what you are looking for?
> 
> The example file GSHP-GLHE.idf illustrates the usage.
> 
> Linda 
> 
> 
> 
> Yahoo! Groups Sponsor
> 
> 
> ADVERTISEMENT
>  
> <http://rd.yahoo.com/M=228862.2128520.3581629.1829184/D=egroupweb/S=1705
> 007389:HM/A=1155066/R=0/*http:/adfarm.mediaplex.com/ad/ck/990-1736-1039-
> 302> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to the Yahoo!
> <http://docs.yahoo.com/info/terms/>  Terms of Service. 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Free $5 Love Reading
Risk Free!
http://us.click.yahoo.com/NsdPZD/PfREAA/Ey.GAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/