By definition, the convection coefficient accounts for all of the
heat transfer effects in the boundary layer near the wall surface.
EnergyPlus uses two sets of correlations to adjust convection
coefficients according to surface roughness, wind speed, and
temperature difference. These correlations, published by ASHRAE,
have been determined through various research projects over the
years. For most applications, the convection coefficients are
generally accepted within the heat transfer community as good
approximations for the total heat transfer. Note that the radiant
transfer from surfaces is handled separately in EnergyPlus and is not
combined into the convection coefficient.
Mike Witte
On 8 Aug 2002, at 2:15, rmp4aup6 wrote:
> Dear everybody:
>
> We can easily get the Surface EXT Convection Coeff from the output of
> energyplus.
>
> And we can easily calculate the Q of heat convection using
> the formula of Q=hcA(ts-tf) where hc=the coeff of convection
> A= the area of surface, ts=temp of surface and tf= tmep of air
> But this is from the viewpoint of theoretical thinking. I am not sure
> the calculation result will be the same as the actual situation.
>
> Besides HVAC system, I wonder E+ can calculate total heat release form
> the building itself.
> Thank you very much.
>
> HSIEH Chun-Ming
>
>
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
4 DVDs Free +s&p Join Now
http://us.click.yahoo.com/pt6YBB/NXiEAA/RN.GAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/