Mike,

You mentioned the controls in the example are complicated. Is there 
an easier way to control the system?

Michelle

--- In EnergyPlus_Support@y..., "Michael J. Witte" <mjwitte@g...> 
wrote:
> See responses mixed in below.
> 
> On 28 Aug 2002, at 15:38, belleengr wrote:
> 
> > Mike,
> > 
> > Thanks for the location of control types in the reference.
> > 
> > I used the Examples\AutoSize\5ZoneAutoDXVAV.idf as my starting 
> > point. As far as I can tell my new file and the original example 
> > file are identical with respect to the zone controls and the 
system 
> > controls. I did change some of the setpoints. Something else 
that is 
> > a bit curious, and makes me think the controls are not working 
> > properly, is the main heating coil is scheduled OFF during he 
> > summer, however it is providing heating when the cooling coil 
> > discharge is low.
> 
> I think there's a mistake in the schedule for the main heating 
coil, 
> it should be HeatingCoilAvailSched, but it's set to 
> ReheatCoilAvailSched.  However, if the setpoints are correct, it 
> should not run anyway.
> 
> > 
> > I am in the midst of reviewing all my setpoints to make sure I 
don't 
> > have a decimal misplaced or something silly.
> > 
> > I will also ask to make sure I understand how the heating and 
> > cooling coils are controlled. For both the DX Cooiling Coil and 
a 
> > Gas Heating Coil there is no CONTROLLER specified, instead they 
use 
> > a SET POINT MANAGER to control the discharge temperature (and 
the 
> > controls are internal to the equipment type.) Should the DX 
Cooling 
> > Coil Control Node and the Gas Heating Coil Control Node be the 
same 
> > as the Node the SET POINT MANAGER specifies through the Set 
Point 
> > Node List?
> > 
> > For example:
> > 
> >   DXSystem:AirLoop,
> >     DX Cooling Coil System 1,  !- Name of DX Cooling Coil System
> >     CoolingCoilAvailSched,  !- Availability schedule
> >     Mixed Air Node 1,  !- DX Cooling Coil System inlet node name
> >     Main Cooling Coil 1 Outlet Node,  !- DX Cooling Coil System 
> > outlet node name
> >     Main Cooling Coil 1 Outlet Node,  !- DX Cooling Coil System 
> > Control Node
> >     COIL:DX:CoolingBypassFactorEmpirical,  !- Cooling coil type
> >     Main Cooling Coil 1;  !- Cooling coil name
> >  
> >   COIL:Gas:Heating,
> >     Main heating Coil 1,  !- Coil Name
> >     ReheatCoilAvailSched,  !- Available Schedule
> >     0.8,  !- Gas Burner Efficiency of the Coil
> >     29000,  !- Nominal Capacity of the Coil {W}
> >     Main Cooling Coil 1 Outlet Node,  !- Coil_Air_Inlet_Node
> >     Main Heating Coil 1 Outlet Node,  !- Coil_Air_Outlet_Node
> >     Main Heating Coil 1 Outlet Node;  !- Coil_Temp_Setpoint_Node
> >  
> >   SET POINT MANAGER:SCHEDULED,
> >     Supply Air Temp Manager 1,  !- Name
> >     TEMP,  !- Control variable
> >     Seasonal Reset Supply Air Temp Sch,  !- Schedule Name
> >     Supply Air Temp Nodes 1;  !- Name of the set point Node List
> >  
> >   NODE LIST,
> >     Supply Air Temp Nodes 1,  !- Node List Name
> >     VAV Sys 1 Outlet Node;  !- Node_ID_1
> >  
> > Which is from my file and is the same for the example file I 
used.
> > 
> 
> The controls in the 5ZoneAutoDXVAV example are a bit complicated.  
As 
> you listed above, there is a SET POINT MANAGER:SCHEDULED which 
> applies a seasonal setpoint schedule to the "VAV Sys 1 Outlet 
Node".
> 
> There is also a SET POINT MANAGER:MIXED AIR which takes the 
setpoint 
> applied to "VAV Sys 1 Outlet Node", subtracts the temperature 
> difference across the supply fan and applies this adjusted 
setpoint 
> to the "Mixed Air Node 1", "Main Cooling Coil 1 Outlet Node", and 
> "Main Heating Coil 1 Outlet Node".  These nodes are then specified 
as 
> the control nodes for the economizer, the heating coil, and the 
> cooling coil.
> 
> The "System Node Setpoint Temp" report variable is helpful in 
seeing 
> what setpoints are being placed on the various nodes.
> 
> Mike
> 
> 
> ========================================================
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...


------------------------ Yahoo! Groups Sponsor ---------------------~-->
4 DVDs Free +s&p Join Now
http://us.click.yahoo.com/pt6YBB/NXiEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/