Re: [EnergyPlus_Support] Questions on report variables - Zone Load Components
Regarding reporting of zone load components . . .
There is currently no zone load component report in EnergyPlus
similar to what DOE-2 had which separated the peak zone load into
components such as conduction through walls, solar gains, internal
loads, etc. With the heat balance method in EnergyPlus, actual load
components are not available which would add up to the peak sizing
load. For example, solar gains fall on one or more surfaces causing
a rise in surface temperature. Some of this rise in surface
temperature increases the zone load immediately, but much of it is
stored in the surface and becomes a load later, some of it may
actually conduct back outside and never become a load, some of it may
radiate to another surface and become a load later. At the same
time all of the other gains in the space are interacting at each
surface. So it is not possible to report true load components.
It is possible to report many of the instantaneous heat gains in
EnergyPlus. This would not be helpful for a peak report since the
loads components peak at different times than the gain, but it might
be useful for a monthly summary component report. Relevant variables
would include:
For windows:
Zone Transmitted Solar[W] (transmitted solar only)
Zone Window Heat Gain[W]
Zone Window Heat Loss[W]
(The previous two are net window heat gain/loss including transmitted
solar)
For internal loads (people, lights, etc.):
Zone-Total Latent Gain[J]
Zone-Total Radiant Heat Gain[J]
Zone-Total Convective Heat Gain[J]
Zone-Total Visible Heat Gain[J]
(the above are totals from all internal gains for the zone)
People-Radiant Heat Gain[J]
People-Convective Heat Gain[J]
People-Sensible Heat Gain[J]
People-Latent Heat Gain[J]
Lights-Total Heat Gain[J]
Lights-Return Air Heat Gain[J]
Lights-Radiant Heat Gain[J]
Lights-Convective Heat Gain[J]
Lights-Visible Heat Gain[J]
Electric Eq-Total Heat Gain[J]
Electric Eq-Radiant Heat Gain[J]
Electric Eq-Convective Heat Gain[J]
Electric Eq-Latent Heat Gain[J]
Electric Eq-Lost Heat Gain[J]
For infiltration and ventilation (only sensible loads are reported
here):
Infiltration-Heat Loss[J]
Infiltration-Heat Gain[J]
Ventilation-Heat Loss[J]
For surface conduction:
Surface conduction is a bit more complicated. If you look at the
convective gain to the zone air from the inside surface, this will
include the effect of transmitted solar and radiant internal loads
which will warm the inside wall surfaces. If you look at the outside
surface heat balance, this includes the impact of convection from
the outside air or conduction from the ground along with solar
incdident on the outside and long-wave radiation to the sky. Since
conduction is not steady state, you cannot simply take conductance
times delta T across the surface. It is probably best to conclude
that surface conduction is the remaining cooling load after
subtracting off the solar and internal gains. If you wish to
examine the surface temperatures, the relevant report variables
would be:
Zone,Average,Outdoor Dry Bulb [C]
Zone,Average,Ground Temperature [C]
Zone,Average,Surface Inside Temperature[C]
Zone,Average,Surface Outside Temperature[C]
Zone,Average,Surface Int Convection Coeff[W/m2-K]
Zone,Average,Surface Ext Convection Coeff[W/m2-K]
Zone,Average,Opaque Surface Inside Face Conduction[W]
The "Opaque Surface Inside Face Conduction" variable is supposed to
be the conduction coming into/out of the inside surface heat balance,
however, I need to check some details before I can say that for sure.
I hope this helps. In a future release, we are planning to implement
a heat gain component report as a standard report.
Mike Witte
On 3 Sep 2002, at 17:55, by way of Linda Lawrie wrote:
> I wonder if you can tell me which report variables (e.g. zone transmitted
> solar, opaque surface inside face conduction, .....etc.) sum together to
> get the zone cooling/heating capacity indicated in the zone sizing report
> or in year simulation output.
> And there is glass solar, glass conduction, wall conduction, roof
> conduction, underground conduction, internal conduction, people load,
> lighting load, equipment load and infiltration load in the peak load report
> of DOE2E. What are the report variables represent the above loads in the
> EnergyPlus?
>
> Thanks!
>
> Lee
>
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
4 DVDs Free +s&p Join Now
http://us.click.yahoo.com/pt6YBB/NXiEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/