Re: [EnergyPlus_Support] VAV system
Currently, EnergyPlus requires that you specify a reheat coil for
each VAV terminal unit, but you can set the coil capacity to zero so
that it does not operate. In the next release, you will be able to
describe a VAV system without reheat coils. For an example of a VAV
system, see EnergyPlus\ExampleFiles\Misc\VAVSingleDuctReheat.idf
Mike Witte
On 3 Oct 2002, at 11:51, rmp4aup6 wrote:
> Dear everybody:
>
> typical three VAV systems are:
> 1. VAV cooling system: only with cooling coil (without reheat)
> 2. VAV reheat system: cooling coil + reheat
> 3. VAV dual duct system: cooling coil + heating coil +reheat
>
> Now, if I just want to simulate VAV cooling system in summer,
> Is it possible? or do we have example?
> ( the system doesn't has heating coil and reheat)
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Sell a Home with Ease!
> http://us.click.yahoo.com/SrPZMC/kTmEAA/MVfIAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Plan to Sell a Home?
http://us.click.yahoo.com/J2SnNA/y.lEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/