Re: [EnergyPlus_Support] Calculate Heating Load
UAdeltaT only applies for steady-state heat transfer. Run with a
DESIGNDAY with constant temperature (Daily Temperature Range = 0), no
solar (Sky Clearness=0), and no internal gains. You should be able
to match the UAdeltaT calculation. Be sure to use the interior and
exterior convection coefficients reported in the output.
Mike Witte
On 9 Oct 2002, at 8:17, gagamere wrote:
> Hi, I have a qustion about heating load calculation.
>
> I usually know that heating load is calculated as formula
>
> Q=U*A*(T_i - T_o)
>
> where, U=1/(R_o + R_i + R_c)
>
> R_o : outer convection heat resistance
> R_i : inner convection heat resistance
> R_c : conduction heat resistance in wall
>
> I review a result of heating rate using Energy Plus and another S/W.
> But I know to differ results.
>
> So, I check the result of Energy Plus.
>
> First, I get a convective coeff in result.
>
> R_i = 1/ Surface Int Convection Coeff
> R_o = 1/ Surface Ext Convection Coeff
> R_c = thickness/Conductivity
>
> Second, I calculate a overall heat conductivit[U] and get heating
> rating, Q.
>
> Then, I know a value calculated by hand is bigger than a value
> calculated by Energy Plus.
>
> Please, tell me a reason.
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Home Selling? Try Us!
> http://us.click.yahoo.com/QrPZMC/iTmEAA/MVfIAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Sell a Home for Top $
http://us.click.yahoo.com/RrPZMC/jTmEAA/MVfIAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/