Re: [EnergyPlus_Support] shape factors
Some clarification on radiant exchange.
View Factors in EnergyPlus
EnergyPlus uses an area weighted approximation to calculate "view
factors" between surfaces within a thermal zone. Each surface sums
up the total area that it can see among the other surfaces. The
approximate view factor from this surface to each other surface is
then the area of the receiving surface over the sum of areas that is
visible to the sending surface.
In order to account in some limited way for the fact that certain
surfaces will not see each other, several assumptions have been built
into this simple view factor approximation. First, a surface cannot
see itself. Second, surfaces with approximately the same azimuth
(facing direction) and tilt ("same" being within one degree) will not
see each other. This means that a window will not see the wall that
it is placed on, for example. Third, floors cannot see each other.
Fourth, if the surface is a floor, ceiling, roof, or internal mass,
the rule for the same azimuth and tilt eliminating radiant exchange
between surface is waived when the receiving surface is floor, roof,
ceiling, or internal mass as long as both surfaces are not floors.
Note that this does not take into account that surfaces may be
"around the corner" from each other and in reality not see each other
at all. Rooms are assumed to be convex rather than concave in this
simple method.
On 7 Oct 2002, at 8:24, Linda Lawrie wrote:
> At 07:02 AM 10/7/2002, Adriana Angelotti wrote:
> >does anybody know if in the radiation exchange between internal
> >surfaces in a zone EnergyPlus calculates shape factors? If yes, are
> >shape factors available as output variables?
>
> No, it does not calculate shape factors.
>
> The program bases view factors on an area weighting and then uses
> Hottel's method to perform the "exact" radiant exchange for gray,
> diffuse surfaces. At some point, we might put in some sort of view
> factor calculation or the ability for the user to specify view
> factors, but that is currently not in the program plan (through
> Version 1.1 -- release Spring 2003).
>
>
>
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/