DOE-2 has several default system part-load curves. The
problem is that DOE-2 curves use deg F inside of E+
deg C for the wet-bulb and dry-bulb. Therefore, one
must change these coefficients. I developed a routine
to do this.
James Trowbridge
--- "Griffith, Brent" <brent_griffith@xxxxxxxx> wrote:
> Greetings,
>
> RE: input for Coil:DX:CoolingBypassFactorEmpirical
>
> Has anyone generated Part Load Fraction Correlation
> functions for larger
> industrial rooftop package units? It seems
> difficult to get part load data
> for specific models. All I have been able to come
> up with is to generate a
> suitable cubic from the Part_Load Factor Curve
> provided as Figure 1. in ARI
> Standard 340/360-2000. This seems to work but I am
> not sure if this is the
> way to go since it often goes way below the E+ limit
> of 0.7. Also I can't
> seem to push the SHR higher than 0.75 which is less
> than what is indicated
> by the equipment specs I am using.
>
> Any ideas? Thanks in advance.
>
> Brent Griffith
>
__________________________________________________
Do you Yahoo!?
Y! Web Hosting - Let the expert host your web site
http://webhosting.yahoo.com/
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/