Greetings,
RE: input for Coil:DX:CoolingBypassFactorEmpirical
Has anyone generated Part Load Fraction Correlation functions for larger
industrial rooftop package units? It seems difficult to get part load data
for specific models. All I have been able to come up with is to generate a
suitable cubic from the Part_Load Factor Curve provided as Figure 1. in ARI
Standard 340/360-2000. This seems to work but I am not sure if this is the
way to go since it often goes way below the E+ limit of 0.7. Also I can't
seem to push the SHR higher than 0.75 which is less than what is indicated
by the equipment specs I am using.
Any ideas? Thanks in advance.
Brent Griffith