The design data in the weather files is from 2001 ASHRAE data. The
datasets use pre-1997 data. The ASHRAE data was completely redone in
the 1997 Handbook of Fundamental. The percentage basis was seasonal
in pre-1997, now it is annual. This, along with some other changes
in method resulted in slightly different values.
"MWS .40%" and PWD .40% are the cooling wind conditions. 3. Almost,
use "Range of DB" data for cooling day, use zero range (constant
temperature) for heating day; clearness, must select, conservative is
zero for heating day, 1.0 for cooling day, clearness ranges from 0.9
at sea level in humid region to 1.1 at high altitude.
On 9 Nov 2002, at 22:08, no_rb wrote:
> If i look at the 5zoneaircooled.idf example - the design day
> information does not completely match the info in the USA_IL_Chicago-
> Ohare_TMY2.epw/rpt file (and it did not match the blastdesign file).
> Also i cannot seem to find wind direction slot for the cooling design
> day in the weather file
>
> am i missing something or does the ashrae design day not provide
> complete information for the eplus design input?
>
> thanks in advance for any pointers.
>
> rohini
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/JjlUgA/vN2EAA/kG8FAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/