Re: [EnergyPlus_Support] Definition



You definitions are correct except for Q.  Q is not a single value 
across the entire wall.  Q_in and Q_out can be different due to 
thermal storage in the middle of the wall.  In fact, Q_in and Q_out 
can be in opposite directions under certain conditions.  For example, 
a south-facing wall is heated by the sun and the temperature in the 
center of the wall starts to rise.  Then the sun moves so that the 
wall is now shaded.  The outside of the wall will begin to cool while 
the center of the wall is still hot.  At this time, heat is flowing 
in two directions away from the hot center.

             _out      _in
               :        :
               :        :
      outside  :        :    inside
               :        :
               :        :
         Q_out <-->     :
               :        :
               :  Q_storage
               :        :
               :     <--> Q_in
               :        :
               :        :
                  wall


On 12 Dec 2002, at 6:22, gagamere gagamere@xxxxxxxxxxx wrote:

> i wondered about the definition of Variable name in Report.
> 
>             _out   _in
>               :     :
>               :     :
>      outside  :     :    inside
>               :     :
>               :     :
>              ---------> Q
>               :     :
>               :     :
>               :     :
>                 wall
> 
> Zone,Average,Surface Inside Temperature[C]         = T_in
> Zone,Average,Surface Outside Temperature[C]        = T_out
> Zone,Average,Surface Int Convection Coeff[W/m2-K]  = h_in
> Zone,Average,Surface Ext Convection Coeff[W/m2-K]  = h_out
> Zone,Average,Opaque Surface Inside Face Conduction[W] 
>    = Q(Heat transfer rate in wall)
> 
> Thank you very much on advance.
> 
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/CBxunD/vN2EAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/CBxunD/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/