Re: [EnergyPlus_Support] return plenum w/ Purchased Air



When you use Purchased Air you do not have an air flow network like you 
have with other systems.  Without the air flowing through the system and 
through the zones, it is not possible to model return air plenums, which 
are zones hooked into the system on either the return or supply air 
paths.  You would have to specify a simple system to achieve interactions 
between plenums, zones, and the HVAC system.

Thanks Richard Liesen



At 11:16 AM 1/16/2003, Griffith, Brent wrote:
>Does anyone know if it is possible to model a return plenum where the
>occupied zones use Purchased Air?  I have pretty large ceiling plenums and
>would like to model their temperatures appropriately.
>
>Brent
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Flexible Keyboard is the ideal accessory for PDA users that are on the move.
http://us.click.yahoo.com/dCBVZC/WnCFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/