The zone multiplier takes the load calculated by the zone that is described
and passes it to the system which in your case would be 6 times. What I am
wondering is if you specified the system to handle 6 times the load? If
you are not using an autosized system then you would have to increase its
capacity accordingly ie. air flow, component sizes, etc. What it looks
like to me is that you increased the zone multiplier and the existing
system took that multiplied and did what it could.
Can you shed some light on this issue?
Thanks Richard Liesen
At 03:59 PM 1/16/2003, Cristina Castaño/LABEIN wrote:
>Hi,
>
>If we use the "multiplier" field equal to 1 the results are the following:
>
>Baseboard: Energy Transfer = 3.624.864 J
>Gas: Plant = 435.550.018 J
>Boilers: Energy Transfer = 391.995.016 J
>Cooling: Energy Transfer = 175.618 J
>Heating: Energy Transfer = 3.800.482 J
>
>
>With the "multiplier" field equal to 6:
>
>Baseboard: Energy Transfer = 11.477.244 J
>Gas: Plant = 515.375.031 J
>Boilers: Energy Transfer = 463.837.528 J
>Cooling: Energy Transfer = 0 J
>Heating: Energy Transfer = 11.477.244 J
>
>We think that this results are wrong because we have six dwellings, and the
>values of the energy transfer of the baseboards, of the gas and boilers are
>too lows. Does Energy Plus consider the consumptions of all the baseboards
>of each dwelling and of the six boilers?.
>
>Best regards,
>Cristina.
>
>
>
>
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Turn flat surfaces into speakers with the Soundbug.
http://us.click.yahoo.com/QWAVSC/onCFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/