Re: [EnergyPlus_Support] Building Overhangs
On 25 Feb 2003, at 3:52, yijun huang wrote:
> Edward has suggested seperate 2D thermal modelling for the roof (using
> THERM) to circumvent the problem, and I was wondering if there are any
> similar strategies that I can use in E+? (Since I don't have support
> in using THERM)
The only thing you can do inside EnergyPlus is to use adjusted
thermal properties for the roof or add a special heat transfer
surface to represent the effect of the overhang. Either approach
would require a separate 2-D or 3-D analysis to determine what the
proper adjustments should be. Perhaps you could find a useful tool
in the USDOE Building Energy Tools Directory:
http://www.eren.doe.gov/buildings/tools_directory/
> Also, what is the difference between the 3 mentioned types of detached
> shading surfaces?
Sorry, I forgot to answer this question.
Surface:Shading:Detached and Surface:Shading:Detached:Fixed are
identical to each other. The coordinates for these surface types are
always in world coordinates.
Surface:Shading:Detached:Building is defined in the building
coordinate system. If relative coordinates are being used, then the
BUILDING North Axis rotation will be applied.
Mike
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/FpY02D/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/