Mike,
Thank you for your explanation. BTW, if I download the new version
of e+, do I need to delete the old one first?
Thanks again!
Li
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> Li: See answers below. Mike
>
>
> On 4 Mar 2003, at 5:24, zl21e zl21e@y... wrote:
>
> > Hello, Everyone,
> > I have some questions about the relative/worldcoordinatesystem.
> >
> > For relative coordinate system, each zone origin coordinates are
> > specified relative to the buiding origin (which is 0,0,0). Every
> > surface vertice's coordinates in that zone are relative to the
zone
> > origin coordinates. For world coordinate system, all zone origin
> > coordinates are (0,0,0). Every vertice's coordinates are absolute
> > coordinates to (0,0,0). Is that right?
>
> Yes, that is correct. In addition, with relative coordinates, the
> building north axis field becomes active.
>
> >
> > In the sample file s1r3DD.idf, relative coordinate system is
used.
> > However, all zone origin coordinates are (0,0,0). Every vertice's
> > coordinates are absolute coordinates to (0,0,0). Is it the same
as
> > world coordinate system?
>
> It is almost the same. With relative coordinates, the building
north
> axis could be applied. With world coordinates, it cannot. (By
the
> way, s1r3DD is quite old, you may need to upgrade versions.)
>
> >
> > In the sample file VAVSingleDuctReheat.idf, world coordinate
system is
> > used. However, each zone origin coordinates are specified
relative
> > to the buiding origin (which is 0,0,0). Every vertice's
coordinates
> > are still absolute coordinates to (0,0,0). Why does this happen?
> >
>
> When daylighting is used, the coordinates for the daylighting
> reference points are always relative to the zone origin. If using
> world coordinates, the zone origins may be left at (0,0,0) and
then
> the daylighting reference points would effectively be in world
> coordinates. Or, the surfaces could be in world coordinates with
non-
> zero zone origins, as in this example. In this case, daylighting
> reference points would be in relative coordinates. In this
> particular example, daylighting is not used, so there is no real
> reason for non-zero zone origins, but it does not affect the
results.
> (Not all of our examples represent the best practice.)
>
>
> > Thank you!
> >
> > Sincerely,
> > Li Zhang
> > Department of Mechanical Engineering
> > Iowa State University
> > Ames, IA 50010
> >
>
>
> ========================================================
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/LIgTpC/vN2EAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/