Further clarification on wind direction for COMIS SITE WIND
CONDITIONS:
The user selects the wind directions and you are supposed to enter
multiple wind condition objects (see I/O ref p. 210) as needed to
specify different conditions on different sides of the building. In
the 3zvent example, there are two such objects:
COMIS SITE WIND CONDITIONS,
0.0, !- Wind direction {deg}
0.20, !- Plan area density {dimensionless}
0.18, !- Exponent of Wind velocity profile {dimensionless}
0.0; !- Surrounding building height {m}
COMIS SITE WIND CONDITIONS,
180.0, !- Wind direction {deg}
0.20, !- Plan area density {dimensionless}
0.32, !- Exponent of Wind velocity profile {dimensionless}
15.0; !- Surrounding building height {m}
On 20 Mar 2003, at 8:18, Achim Geissler wrote:
>
> > #1:
> > COMIS Site Wind Conditions
> > Field: Wind direction
> > Am I supposed to get the wind direction from weather file?
> > Is the wind direction available in EnergyPlus weather file?
> Yes, wind direction and wind speed are in the EPW file (fields N20 and
> N21)
>
> > #2: Taken from 3zvent.idf
> > COMIS SIMULATION,
> > 0.14, !- Wind velocity profile exponent {dimensionless}
> This is the wind profile exponent of the site where wind speed (and
> direction) are "being measured"
>
> > COMIS SITE WIND CONDITIONS,
> > 0.32, !- Exponent of Wind velocity profile {dimensionless}
> This is the wind profile exponent of the building site.
>
> > Does it conflict? If yes, which one overcomes the other?
> No, the are both used to transform meteorological wind speed to site
> wind speed by 1. calculating the meteorological wind speed for
> "boundary thickness height" (usually 60 or more meters) at met.
> station site 2. calculating the site wind speed for building height
>
> Hope this helps.
>
> Regards,
> Achim Geissler
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/