[EnergyPlus_Support] Re: Further clarification on wind direction for COMIS SITE WIND CONDITIONS
So, the following, which is correct?
#1:EnergyPlus/COMIS doesn't use the wind direction data from
weather/EPW file. It only uses the wind directions from the user
input in IDF file.
#2:EnergyPlus/COMIS does use the wind direction data from weather/EPW
file. It gets the wind direction from weather/EPW and get other
values by interpolating between the two COMIS SITE WIND CONDITIONS.
Thanks a lot,
Ming
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> Further clarification on wind direction for COMIS SITE WIND
> CONDITIONS:
>
> The user selects the wind directions and you are supposed to enter
> multiple wind condition objects (see I/O ref p. 210) as needed to
> specify different conditions on different sides of the building.
In
> the 3zvent example, there are two such objects:
>
> COMIS SITE WIND CONDITIONS,
> 0.0, !- Wind direction {deg}
> 0.20, !- Plan area density {dimensionless}
> 0.18, !- Exponent of Wind velocity profile {dimensionless}
> 0.0; !- Surrounding building height {m}
>
> COMIS SITE WIND CONDITIONS,
> 180.0, !- Wind direction {deg}
> 0.20, !- Plan area density {dimensionless}
> 0.32, !- Exponent of Wind velocity profile {dimensionless}
> 15.0; !- Surrounding building height {m}
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/