Re: [EnergyPlus_Support] Vav with purchased::chilled water



Lourenço:  

Purchase chilled water is equivalent to a chiller, so you need a 
chiller water coil and a chilled water plant loop.  See 5ZoneAuto for 
an example.

Mike


On 17 Apr 2003, at 13:05, nuno lourenço wrote:

> Hi,
> 
> I want to model a VAV for one zone with purchased cooling. I tried to
> adapt the example file 5ZoneAutoDxVAV to my case by replacing the DX
> coil with purchased chilled water but failed. Could anyone give some
> hints about this?
> 
> 
> Thanks in advance,
> 
> Lourenço
> 
> 
> 
> 
> 
> _________________________________________________________________ MSN
> Messenger: converse com os seus amigos online.
> http://messenger.msn.com.br
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/xaxhjB/hdqFAA/VygGAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/VygGAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/