Re: [EnergyPlus_Support] describe a window air conditioner
The component type field in the equipment list must be a valid
componente type, in this case "AIR CONDITIONER:WINDOW:CYCLING".
See example file \EnergyPlus\ExampleFiles\Misc\WindAC.idf
Mike
On 19 Jun 2003, at 9:20, landlord0l wrote:
> Dear all,
>
> I am a beginner for EnergyPlus. I tried to model a room equiped with a
> window-type air conditioner and encountered a problem. The following
> message was shown:
>
> ** Severe ** Only 1st Node used from List=INDOOR AIR-1 for Zone Equip
> Manager=MAIN BEDROOM_1
> ** Severe ** During Zone Equipment List Input, Invalid Component
> Type input=WINDOW AC
> ** ~~~ ** Component name=RAC-1
>
> I have described a window air conditoner component named RAC-1. Is
> this caused by some other missing description?
>
> Thanks.
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Looking for the latest Free IT White Papers?
> Visit SearchNetworking.com to access over 500 white papers. Get
> instant access at SearchNetworking.com Today
> http://us.click.yahoo.com/YyjvfD/OLNGAA/uitMAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Looking for the latest Free IT White Papers?
Visit SearchSecurity.com to access over 500 white papers.
Get instant access at SearchSecurity.com Today
http://us.click.yahoo.com/ayjvfD/QLNGAA/uitMAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/