AW: [EnergyPlus_Support] radiation terms
What about the IR heat exchange? The IR heat exchange with the sky can
be estimated from the known sky and surface temperature. In the case of
the IR heat exchange with the ground, do the ground temperatures from
the weather file have to be accounted for? What is the IR emittance
coefficient for the ground like in EPlus?
Thanks
Alexander
-----Ursprüngliche Nachricht-----
Von: Frederick Winkelmann [mailto:FCWinkelmann@xxxxxxx]
Gesendet: Donnerstag, 19. Juni 2003 22:07
An: EnergyPlus_Support@xxxxxxxxxxxxxxx
Betreff: Re: [EnergyPlus_Support] radiation terms
The resported sky diffuse, ground diffuse and beam radiation incident on
a surface are all solar quantities. They should be
multiplied by the solar absorptance of the surface to get the amount of
each that is absorbed.
Fred Winkelmann
idoebber wrote:
> I am trying to calculate the total radiation incident on a surface
that is
> absorbed. The outputs for radiation incident on a surface are sky
diffuse,
> ground diffuse, and solar beam. Yet the absorptance constants for the
> building material are thermal, solar, and visible. How do I calculate
the
> fraction of each radiation that is absorbed.
>
> Thanks
> Ian
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
appropriate folder in the Files are of the Support Web Site.
>
>
>
> Your use of Yahoo! Groups is subject to
http://docs.yahoo.com/info/terms/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to
http://docs.yahoo.com/info/terms/
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Looking for the latest Free IT White Papers?
Visit SearchMobileComputing.com to access over 500 white papers.
Get instant access at SearchMobileComputing.com Today
http://us.click.yahoo.com/ZyjvfD/PLNGAA/uitMAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/