Also check to make sure that the ventilation is operating as desired. 
 There could be a problem with the control specifications on 
ventilation.

On 26 Jun 2003, at 8:30, Edward Lyon wrote:

> Relative humidity is temperature dependent.  If your zone temperature
> is higher than outside due to solar gains, there will be a depression
> in interior RH even though the moisture levels of interior and
> exterior air are the same.  Try looking at dew point temperatures to
> see if the interior is getting the outside moisture.  At 12 ACH with
> no AC the interior and exterior dew point temperatures should be
> essentially equal.  The DX AC window air conditioner can also give you
> some poor results for RH control also.  An over-sized unit that runs
> short cycles will typically dehumidify better in the model than a load
> matched system that runs full time.  In reality, the short cycle
> operation would produce almost no dehumidification.  Finally, if the
> moisture models do work properly, you may need to model several days
> to see the results you want.  In a recent test I performed we
> simulated occupancy moisture loads in two apartments, one with good
> ventilation and one with poor ventilation.  The data indicated that
> the poorly ventilated unit took about 3 days to "store up" moisture in
> the interior finishes before it reached a cyclical equilibrium with
> the induced load.  Since you can not be completely certain where the
> wall moisture storage starts after model warmup, you must run the
> simulation several days to reach your actual induced conditions,
> longer if you have high storage systems like masonry.  In fact, a
> precast concrete or concrete masonry unit wall system may take a year
> or more to equalize with its surroundings.  I'm not sure that the
> transfer function method implemented for moisture storage in
> EnergyPlus is as accurate for heavy weight construction as it could be
> for light weight stud wall systems which respond faster to ambient RH
> changes.  
> 
> Ned Lyon
> 
> Senior Staff Engineer
> Simpson Gumpertz & Heger Inc.
> 
> 41 Seyon Street
> Building #1, Suite 500
> Waltham, MA  02453
> 
> Phone:  781-907-9000
> Fax:  781-907-9009
> 
> 
> >>> zplin99@xxxxxxxxxxx 06/26/03 12:02AM >>>
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Looking for the latest Free IT White Papers?
> Visit SearchNetworking.com to access over 500 white papers. Get
> instant access at SearchNetworking.com Today
> http://us.click.yahoo.com/YyjvfD/OLNGAA/uitMAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Looking for the latest Free IT White Papers?
Visit SearchMobileComputing.com to access over 500 white papers.
Get instant access at SearchMobileComputing.com Today
http://us.click.yahoo.com/ZyjvfD/PLNGAA/uitMAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/