Hi, Ned,
Thank you very much for your helpful suggestions.
The ventilation was operating as desired, which may be confirmed by the
output variable: ventilation-volume. The moisture model also did work
properly, since the zone air humidity ratio equal to the outdoor
humidity ratio within 2 hours after the AC was OFF. You mentioned that
some error may be caused by the DX AC window conditioner. I guess this
is the case in my simulation. What I simulated was the nighttime
operating period, however, the window AC was sized by the total cooling
load on design summer day. Therefore, the “over-size” unit was always
run short cycles during nighttime. Do you think this deviation in RH
control for DX AC window air conditioner is big enough?
Thanks again.
Zhongping
-----Original Message-----
From: Michael J. Witte [mailto:mjwitte@xxxxxxxx]
Sent: Thursday, June 26, 2003 10:14 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] About the zone air relative humidity
for a zone with windoow air conditioner
Also check to make sure that the ventilation is operating as desired.
There could be a problem with the control specifications on
ventilation.
On 26 Jun 2003, at 8:30, Edward Lyon wrote:
> Relative humidity is temperature dependent. If your zone temperature
> is higher than outside due to solar gains, there will be a depression
> in interior RH even though the moisture levels of interior and
> exterior air are the same. Try looking at dew point temperatures to
> see if the interior is getting the outside moisture. At 12 ACH with
> no AC the interior and exterior dew point temperatures should be
> essentially equal. The DX AC window air conditioner can also give you
> some poor results for RH control also. An over-sized unit that runs
> short cycles will typically dehumidify better in the model than a load
> matched system that runs full time. In reality, the short cycle
> operation would produce almost no dehumidification. Finally, if the
> moisture models do work properly, you may need to model several days
> to see the results you want. In a recent test I performed we
> simulated occupancy moisture loads in two apartments, one with good
> ventilation and one with poor ventilation. The data indicated that
> the poorly ventilated unit took about 3 days to "store up" moisture in
> the interior finishes before it reached a cyclical equilibrium with
> the induced load. Since you can not be completely certain where the
> wall moisture storage starts after model warmup, you must run the
> simulation several days to reach your actual induced conditions,
> longer if you have high storage systems like masonry. In fact, a
> precast concrete or concrete masonry unit wall system may take a year
> or more to equalize with its surroundings. I'm not sure that the
> transfer function method implemented for moisture storage in
> EnergyPlus is as accurate for heavy weight construction as it could be
> for light weight stud wall systems which respond faster to ambient RH
> changes.
>
> Ned Lyon
>
> Senior Staff Engineer
> Simpson Gumpertz & Heger Inc.
>
> 41 Seyon Street
> Building #1, Suite 500
> Waltham, MA 02453
>
> Phone: 781-907-9000
> Fax: 781-907-9009
>
>
> >>> zplin99@xxxxxxxxxxx 06/26/03 12:02AM >>>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Looking for the latest Free IT White Papers?
> Visit SearchNetworking.com to access over 500 white papers. Get
> instant access at SearchNetworking.com Today
> http://us.click.yahoo.com/YyjvfD/OLNGAA/uitMAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
Yahoo! Groups Sponsor
<http://rd.yahoo.com/M=249982.3179269.4495679.1261774/D=egroupweb/S=1705
007389:HM/A=1524963/R=0/SIG=12ongbbsq/*http:/hits.411web.com/cgi-bin/aut
oredir?camp=556&lineid=3179269∝=egroupweb&pos=HM>
<http://us.adserver.yahoo.com/l?M=249982.3179269.4495679.1261774/D=egrou
pmail/S=:HM/A=1524963/rand=765621802>
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to the Yahoo!
<http://docs.yahoo.com/info/terms/> Terms of Service.
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Looking for the latest Free IT White Papers?
Visit SearchMobileComputing.com to access over 500 white papers.
Get instant access at SearchMobileComputing.com Today
http://us.click.yahoo.com/ZyjvfD/PLNGAA/uitMAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/