I changed the design day weather data and it works. Thank you, Mike.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "zhaicq98" <chaoqinz@a...> 
wrote:
> Is it to say that I have to change my design day weather data in 
> order to correctly size the reheat coil?
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> <mjwitte@g...> wrote:
> > That means your design days do not cause a heating load, so the 
> > reheat coil is sized to zero.  
> > 
> > On 14 Jul 2003, at 17:57, zhaicq98 wrote:
> > 
> > > Oh, it is always zero.
> > > What is wrong? 
> > > 
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> > > <mjwitte@g...> wrote:
> > > > Chaoqin:
> > > > 
> > > > First, check the sizing reports in the eio file to see if the 
> > > reheat 
> > > > coil is sized to something greater than zero.  Then check the 
> > > > thermostat controls.
> > > > 
> > > > Mike
> > > > 
> > > > p.s.  I will be out of the office July 16-27.  E-mail sent to 
> > > > mjwitte@g... will not be seen until I return.  Use energyplus-
> > > > support@g... or EnergyPlus_Support@xxxxxxxxxxxxxxx so that 
> others
> > > > can respond.
> > > > 
> > > > 
> > > > On 14 Jul 2003, at 14:54, zhaicq98 wrote:
> > > > 
> > > > > Hi,
> > > > > 
> > > > > I have a system that is exactly the same as that in example 
> file
> > > > > 5ZoneAutoDXVAV.idf. I also created my input file according 
to 
> this
> > > > > example file. However, it seems that the reheat coil in my 
> single 
> > > duct
> > > > > VAV:reheat does not work. I output the heating coil energy 
> and it 
> > > is
> > > > > always zero. I also output the zone air temperature, and it 
> is far
> > > > > below the setpoint. I tried the example file, and it works 
> well 
> > > on my
> > > > > computer. Can anyone give me any information about what the 
> > > problem
> > > > > might be?
> > > > > 
> > > > > Thanks,
> > > > > Chaoqin
> > > > > 
> > > > > 
> > > > > 
> > > > > ------------------------ Yahoo! Groups Sponsor
> > > > > ---------------------~--> Buy 1, Get 1 FREE Control 
Cravings 
> & 
> > > Hunger
> > > > > EZ! Fast Acting Natural Oral Spray - $19.97
> > > > > http://www.challengerone.com/t/l.asp?
> cid=2866&lp=ezappetite3.html
> > > > > http://us.click.yahoo.com/rJIe0D/99VGAA/ySSFAA/dkFolB/TM
> > > > > ------------------------------------------------------------
--
> ----
> > > ---> > ->
> > > > > 
> > > > > To unsubscribe from this group, send an email to:
> > > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > > > 
> > > > > The primary EnergyPlus web site is found at:
> > > > > http://www.energyplus.gov
> > > > > 
> > > > > The group web site is:
> > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > > 
> > > > > Attachments are not allowed -- please post any files to the
> > > > > appropriate folder in the Files are of the Support Web Site.
> > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > 
> > > > > Your use of Yahoo! Groups is subject to
> > > > > http://docs.yahoo.com/info/terms/ 
> > > > > 
> > > > 
> > > > 
> > > > 
> > > > ========================================================
> > > > EnergyPlus Testing and Support      
> > > > EnergyPlus-Support@g...
> > > 
> > > 
> > > ------------------------ Yahoo! Groups Sponsor
> > > ---------------------~--> Free shipping on all inkjet cartridge 
&
> > > refill kit orders to US & Canada. Low prices up to 80% off. We 
> have
> > > your brand: HP, Epson, Lexmark & more.
> > > http://www.c1tracking.com/l.asp?cid=5510
> > > http://us.click.yahoo.com/GHXcIA/n.WGAA/ySSFAA/dkFolB/TM
> > > ----------------------------------------------------------------
--
> ---> > ->
> > > 
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > 
> > > Attachments are not allowed -- please post any files to the
> > > appropriate folder in the Files are of the Support Web Site.
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > Your use of Yahoo! Groups is subject to
> > > http://docs.yahoo.com/info/terms/ 
> > >


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Naturally Painless & Spray Away Backaches & Joint Pain. $19.97
http://www.challengerone.com/t/l.asp?cid=2867&lp=m331.html
http://us.click.yahoo.com/tJIe0D/79VGAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/