Thanks Richard,

I followed your advised and checked the air enthalpies of all the nodes
involved. Then I realized that the fancoil cooling power rates refer to the
effect of the fancoil on the controlled zone. On the other side, the cooling
coil power rates refer to the energy balance inside the fancoil. As I was
working on an open loop system, there is no relation between this variables.

Finally, I didn't find any documentation about how dehumidification is
managed in a simple cooling coil. I would appreciate if anybody could tell
me.

Thanks in advance,


 -----Mensaje original-----
De: Richard J. Liesen [mailto:rliesen@xxxxxxxx]
Enviado el: miércoles, 16 de julio de 2003 18:55
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx; EnergyPlus_Support@yahoogroups.
com
Asunto: Re: [EnergyPlus_Support] Fancoil total cooling power rate & total
water cooling coil power rate


  Miguel,
  The first thing you need to do is take one of your Fan Coil units and set
  the Maximum Outside Air = 0.0 and then look at the reports.  When you do
  this then you will see exactly what you expect in the reports, ie. Total >
  Sensible, and Total Water Coil Cooling Rate = Fan Coil Total Cooling Rate
+
  Fan Power. After you are confident that the variables are reporting what
  you expect then add the mixed air stream to the results.  Total Q across
  the unit is just the enthalpy change and the sensible Q across the unit is
  the change in enthalpy at a constant inlet humidity ratio.

  Total Enthalpy
  QTotUnitOut = AirMassFlow * (Node(OutletNode)%Enthalpy -
  Node(InletNode)%Enthalpy)

  Sensible Change
  QUnitOut = AirMassFlow *
  (PsyHTW(Node(OutletNode)%Temp,Node(InletNode)%HumRat)  &
                             -
  PsyHTW(Node(InletNode)%Temp,Node(InletNode)%HumRat))

  Remember that these variables are looking across the entire unit including
  the mixed air contributions.

  For the example case that I was looking at and when you look at and report
  the Temperature and Humidity Ratio at each node location, ie. FanCoil1
  #          Description
  5,      ZONE1FANCOILAIRINLETNODE
  56, ZONE1FANCOILEXHNODE
  1,      ZONE1FANCOILOAINNODE
  59, ZONE1FANCOILOAMIXEROUTLETNODE
  62, ZONE1FANCOILFANOUTLETNODE
  65, ZONE1FANCOILCCOUTLETNODE
  4,      ZONE1FANCOILAIROUTLETNODE

  You will find that the Latent Load added through the mixed air is greater
  than what is extracted by the Cooling Coil.


  Thanks
  Dr. Richard J. Liesen  Ph.D. M.E.
  Associate Director, Building Systems Laboratory
  Department of Mechanical and Industrial Engineering
  University of Illinois at Urbana-Champaign
  * * * * * * * * * * * * * * * * * * * * * * *



  t 02:54 PM 7/16/2003, Miguel Angel Pascual wrote:
  >hello,
  >
  >I'm running a simulation with a FAN COIL UNIT:4 PIPE with a
  >COIL:Water:SimpleCooling object and  I have noticed an important
difference
  >between the variables "Fancoil total cooling power rate" and  "total
water
  >cooling coil power rate". I thought that both variables should be very
  >similar, but the difference is much bigger than the electric power fan.
  >
  >I am taking 100% outside air to the fancoil, and under condensing
conditions
  >"Fancoil total cooling power rate" and "Fancoil sensible cooling power
rate"
  >are almost the same. In some cases, the total cooling power rate was
smaller
  >than the sensible fancoil variables.
  >
  >Does anybody know what is going on?
  >
  >
  >Miguel Ángel Pascual
  >Dtor. Ingeniería
  >MIYABI
  >mapascual@xxxxxxxxxxxx
  >948 203 644
  >
  >
  >
  >[Non-text portions of this message have been removed]
  >
  >
  >
  >To unsubscribe from this group, send an email to:
  >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
  >
  >The primary EnergyPlus web site is found at:
  >http://www.energyplus.gov
  >
  >The group web site is:
  >http://groups.yahoo.com/group/EnergyPlus_Support/
  >
  >Attachments are not allowed -- please post any files to the appropriate
  >folder in the Files are of the Support Web Site.
  >
  >
  >
  >
  >
  >
  >Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/



        Yahoo! Groups Sponsor
              ADVERTISEMENT




  To unsubscribe from this group, send an email to:
  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

  The primary EnergyPlus web site is found at:
  http://www.energyplus.gov

  The group web site is:
  http://groups.yahoo.com/group/EnergyPlus_Support/

  Attachments are not allowed -- please post any files to the appropriate
folder in the Files are of the Support Web Site.






  Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.



[Non-text portions of this message have been removed]


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/sOykFB/k9VGAA/ySSFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/