Re: [EnergyPlus_Support] saving energy with change setpoint thermostat
The warnings show that your simulation is not converging and so it is
not producing valid results. There are many examples in the
EnergyPlus\ExampleFiles folder of system with chilers:
5ZoneWaterCooled.idf and VAVSingleDuctReheat.idf - variable volume
single duct system
DDAutoSize.idf - constant volume dual duct system
Mike
On 4 Sep 2003, at 16:49, Tata Yohana wrote:
> Dear All,
>
> I am using EnergyPlus for calculate energy consumption of the
> building. My model just for cooling load operation, and the building
> using chiller for cooling loop. In setpoint thermostat using single
> cooling setpoint with control type 2. I have running the simulation
> for setpoint thermostat 22 C during occupied hours (from hour 5-18)
> and 27 C otherwise, and I have get total electricity facility (J). But
> when I reduce cooling setpoint from 22 C to 24 C during occupied
> hours, total electricity facility not change. I can't get saving
> energy from reduce setpoint thermostat.
>
> After running simulation, I get this warning :
> ---------------------------------------------------------------
> ************* Testing Individual Branch Integrity
> ************* All Branches passed integrity testing
> ************* Testing Individual Supply Air Path Integrity
> ************* All Supply Air Paths passed integrity testing
> ************* Testing Individual Return Air Path Integrity
> ************* All Return Air Paths passed integrity testing
> ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 04:15 - 04:30
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 04:30 - 04:45
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 04:45 - 05:00
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 05:00 - 05:15
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 05:15 - 05:30
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 05:30 - 05:45
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 05:45 - 06:00
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 06:00 - 06:15
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 06:15 - 06:30
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 06:30 - 06:45
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 06:45 - 07:00
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 07:00 - 07:15
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 07:15 - 07:30
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> loops, SRJY, 07/21 07:15 - 07:17
> ** Warning ** SimHVAC: Exceeding max iterations continues...50
>
> ----------------------------------------------------------------- Can
> any one help me for this problem? And can I get some example for
> simulation like this?
>
> I do hope for a reply in the future. Thank you very much for your
> concern
>
> Tata
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/