[EnergyPlus_Support] Re: saving energy with change setpoint thermostat
Thank you Mr. Mike,
I have repair my model and running simulation.
But I get a dramatic result in energy savings.
Total electricity facility is reduced 10 % for every 1 ^C difference
in thermostat setting. I don't know it's possible or not ?
Can you tell me calculation method for cooling load in EnergyPlus
v1.1 ?
Tata
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> The warnings show that your simulation is not converging and so it
is
> not producing valid results. There are many examples in the
> EnergyPlus\ExampleFiles folder of system with chilers:
>
> 5ZoneWaterCooled.idf and VAVSingleDuctReheat.idf - variable volume
> single duct system
>
> DDAutoSize.idf - constant volume dual duct system
>
> Mike
>
>
> On 4 Sep 2003, at 16:49, Tata Yohana wrote:
>
> > Dear All,
> >
> > I am using EnergyPlus for calculate energy consumption of the
> > building. My model just for cooling load operation, and the
building
> > using chiller for cooling loop. In setpoint thermostat using
single
> > cooling setpoint with control type 2. I have running the
simulation
> > for setpoint thermostat 22 C during occupied hours (from hour 5-
18)
> > and 27 C otherwise, and I have get total electricity facility
(J). But
> > when I reduce cooling setpoint from 22 C to 24 C during occupied
> > hours, total electricity facility not change. I can't get saving
> > energy from reduce setpoint thermostat.
> >
> > After running simulation, I get this warning :
> > ---------------------------------------------------------------
> > ************* Testing Individual Branch Integrity
> > ************* All Branches passed integrity testing
> > ************* Testing Individual Supply Air Path Integrity
> > ************* All Supply Air Paths passed integrity testing
> > ************* Testing Individual Return Air Path Integrity
> > ************* All Return Air Paths passed integrity testing
> > ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> > ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> > ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> > ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> > ** Warning ** tp12c0: not converged in 8 CoolCoilErrs
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 04:15 - 04:30
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 04:30 - 04:45
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 04:45 - 05:00
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 05:00 - 05:15
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 05:15 - 05:30
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 05:30 - 05:45
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 05:45 - 06:00
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 06:00 - 06:15
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 06:15 - 06:30
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 06:30 - 06:45
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 06:45 - 07:00
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 07:00 - 07:15
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 07:15 - 07:30
> > ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC
> > loops, SRJY, 07/21 07:15 - 07:17
> > ** Warning ** SimHVAC: Exceeding max iterations continues...50
> >
> > -----------------------------------------------------------------
Can
> > any one help me for this problem? And can I get some example for
> > simulation like this?
> >
> > I do hope for a reply in the future. Thank you very much for your
> > concern
> >
> > Tata
> >
> >
> >
> > ------------------------ Yahoo! Groups Sponsor
> > ---------------------~--> Buy Ink Cartridges or Refill Kits for
Your
> > HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on
orders
> > $50 or more to the US & Canada.
> > http://www.c1tracking.com/l.asp?cid=5511
> > http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> > ------------------------------------------------------------------
---~
> > ->
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to
> > http://docs.yahoo.com/info/terms/
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/