Re: [EnergyPlus_Support] Ground Temperature
You are correct that the current recommended use is to specify the
average temperatures from the slab program for the ground
temperatures. In the future, we plan to add options for specifying
different ground temperatures for difference surfaces. For now, you
could use OTHER SIDE COEFFICIENTS to specify a fixed temperature on
the outside of the core slab and then put the perimeter ground
temperatures from the slab program into the GROUND TEMPERATURES
object and have your perimeter slabs exposed to ground.
Mike
On 4 Sep 2003, at 19:27, waspoorboy wrote:
> In E+, there's a field for specifying ground temp.
> For a very big slab on grade 1 floor building, 100,000+ sqft.
> The core ground temp will be different from perimeter ground temp.
> Perimeter ground temp will be close to "undisturbed" ground temp.
> Core ground temp will be close to indoor air temp.
> So, is the Average ground temp calculated by "slab.exe" the solution
> which should be filled in the ground temp field in E+ idf file ? Is
> there any suggestions how accurate slab.exe is ?
>
> For the very big slab on grade 1 floor building, 100,000+ sqft.
> interior zone floor will not have ground temp = avg. ground temp.
> exterior zone floor will not have ground temp = avg. ground temp.
> So then the load calc and system sizing for zones in E+, which uses
> average ground temp, will be off some error. The error in the 100,000+
> sqft case is "big".
>
> Is there any way to deal with it ?
>
>
>
>
>
>
>
> >Msg#1005<mjwitte@g...> wrote:
> >The ground underneath a building tends to be much closer to
> >the indoor temperature of the building than the undisturbed
> >temperatures.
>
> >There is a utility included with EnergyPlus called "slab.exe" in the
> >EnergyPlus\PreProcess\GrndTempCalc\ folder. This utility calculates
> >monthly core, perimeter, and average ground temperatures...
>
> >Msq#250<mjwitte@g...> wrote:
> >If you have no other data, a reasonable assumption is to use 18C for
> > all 12 months for the ground temperature and to describe the slab
> >floor construction with concrete as the outside layer (no soil layer
> > as some of the examples show). This is reasonable, because the
> > ground temperature under the main portion of the floor of a
> > conditioned space tends to stabilize to a temperature driven by the
> > indoor conditioned space temperature.
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for Your HP, Epson, Canon or Lexmark
Printer at Myinks.com. Free s/h on orders $50 or more to the US & Canada. http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/