RE: [EnergyPlus_Support] - Uploaded Dual Duct file
Thanks, Mike. With regards to the set point managers, I am now unsure as to how to connect the humidifier up to multiple zones. On relection, the "maximum iterations exceeded" file could be caused by the air loop outlet node being referenced so often. I figured referring the zones to the same node would in a sense create a splitter for humidification. Is there an example file available where more than one zone is served by a humidifier? Can the humidifier serve the zones without a set point manager? After all, there is already a setpoint outlined in the "Humidistat" object. Thanks in advance,
Sam Roose
-----Original Message-----
From: Michael J. Witte [mailto:mjwitte@xxxxxxxx]
Sent: Tue 9/09/2003 5:20 a.m.
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc:
Subject: RE: [EnergyPlus_Support] - Uploaded Dual Duct file
A dual duct system needs two air branches, each with an exit node.
These exit nodes are listed in a node list which is specified as the
"AirLoop Outlet Nodes" list in the AIR PRIMARY LOOP object. These
nodes, and the order in which they are listed, must correspond with
the nodes in the "SupplyAirPath ZoneEquipGroup Inlet Nodes" list.
I only see one air branch in your simulation. You need a branch for
the hot side and a branch for the cold side. See one of the dual
duct examples, such as
\EnergyPlus\ExampleFiles\Misc\DualDuctVarVolDamper.idf
Also, I see many set point managers all acting on the same node (Air
Loop Outlet Node). This will not work as you expect. Each setpoint
manager will overwrite the value placed on the setpoint node, so only
the last one in the list will actually control the node.
Mike
On 7 Sep 2003, at 16:09, Samuel Roose wrote:
> I have two issues with a file I have just uploaded (dualduct.idf). One
> is that I am trying to run the dual duct system and maintain the air
> loop - I get this error message:
>
> ** Severe ** Air System:number of air system exit nodes must match
> number of zone equip inlet nodes ** Severe ** Branch for Air
> System=TYPICAL TERMINAL REHEAT 1, has an error. ** ~~~ **
> Probable missing or misspelled node referenced in the branch(es):
> ** ~~~ ** Possible Error in Branch Object=AIR LOOP MAIN BRANCH
> ** Fatal ** Errors found getting Air Primary Loop
>
> It is not clear to me which nodes to put where for this one.
>
> The other issue is that I am trying to gain energy consumption data
> for the two gas boilers in the file. I have put a "Gas: Facility"
> meter in, but this does not register any values in the output. The hot
> water loop demand results also seems to be cumulative. Is there an
> output which can give me the gas consumption per hour for these
> boilers, or are the boilers in the file not functioning for some
> reason?
>
> Thanks in advance,
>
> Sam Roose
> Victoria University of Wellington
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
Yahoo! Groups Sponsor
ADVERTISEMENT
click here <http://rd.yahoo.com/M=251812.3170658.4537139.1261774/D=egroupweb/S=1705007389:HM/A=1693352/R=0/SIG=11tralmvc/*http://www.netflix.com/Default?mqso=60178293&partid=3170658>
<http://us.adserver.yahoo.com/l?M=251812.3170658.4537139.1261774/D=egroupmail/S=:HM/A=1693352/rand=279326846>
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> .
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/