RE: [EnergyPlus_Support] - Uploaded Dual Duct file



My apologies for the dealayed response.  SET POINT MANAGER:SINGLE 
ZONE MIN HUM is used to control a humidifier for a single zone.  ZONE 
CONTROL:HUMIDISTAT is used to control unitary equipment for 
dehumidification.  These are both single-zone objects.  There is no 
multiple-zone humidity control currently available.

Mike


On 9 Sep 2003, at 17:27, Samuel Roose wrote:

> Thanks, Mike. With regards to the set point managers, I am now unsure
> as to how to connect the humidifier up to multiple zones. On
> relection, the "maximum iterations exceeded" file could be caused by
> the air loop outlet node being referenced so often. I figured
> referring the zones to the same node would in a sense create a
> splitter for humidification. Is there an example file available where
> more than one zone is served by a humidifier? Can the humidifier serve
> the zones without a set point manager? After all, there is already a
> setpoint outlined in the "Humidistat" object. Thanks in advance,
> 
> Sam Roose    
> 
>  -----Original Message----- 
>  From: Michael J. Witte [mailto:mjwitte@xxxxxxxx] 
>  Sent: Tue 9/09/2003 5:20 a.m. 
>  To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
>  Cc: 
>  Subject: RE: [EnergyPlus_Support] - Uploaded Dual Duct file
> 
> 
>  A dual duct system needs two air branches, each with an exit node.  
>  These exit nodes are listed in a node list which is specified as the 
>  "AirLoop Outlet Nodes" list in the AIR PRIMARY LOOP object.  These 
>  nodes, and the order in which they are listed, must correspond with 
>  the nodes in the "SupplyAirPath ZoneEquipGroup Inlet Nodes" list.
> 
>  I only see one air branch in your simulation.  You need a branch for 
>  the hot side and a branch for the cold side.  See one of the dual 
>  duct examples, such as
> 
>  \EnergyPlus\ExampleFiles\Misc\DualDuctVarVolDamper.idf
> 
>  Also, I see many set point managers all acting on the same node (Air 
>  Loop Outlet Node).  This will not work as you expect.  Each setpoint 
>  manager will overwrite the value placed on the setpoint node, so only
>  the last one in the list will actually control the node.
> 
>  Mike
> 
> 
>  On 7 Sep 2003, at 16:09, Samuel Roose wrote:
> 
>  > I have two issues with a file I have just uploaded (dualduct.idf).
>  One > is that I am trying to run the dual duct system and maintain
>  the air > loop - I get this error message: > >    ** Severe  ** Air
>  System:number of air system exit nodes must match >    number of zone
>  equip inlet nodes ** Severe  ** Branch for Air >    System=TYPICAL
>  TERMINAL REHEAT 1, has an error. **   ~~~   ** >    Probable missing
>  or misspelled node referenced in the branch(es): >    **   ~~~   **
>  Possible Error in Branch Object=AIR LOOP MAIN BRANCH >    **  Fatal 
>  ** Errors found getting Air Primary Loop > > It is not clear to me
>  which nodes to put where for this one. > > The other issue is that I
>  am trying to gain energy consumption data > for the two gas boilers
>  in the file. I have put a "Gas: Facility" > meter in, but this does
>  not register any values in the output. The hot > water loop demand
>  results also seems to be cumulative. Is there an > output which can
>  give me the gas consumption per hour for these > boilers, or are the
>  boilers in the file not functioning for some > reason? > > Thanks in
>  advance, > > Sam Roose > Victoria University of Wellington > >
>  ------------------------ Yahoo! Groups Sponsor >
>  ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
>  > HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on
>  orders > $50 or more to the US & Canada. >
>  http://www.c1tracking.com/l.asp?cid=5511 >
>  http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM >
>  ---------------------------------------------------------------------
>  ~ > -> > > To unsubscribe from this group, send an email to: >
>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx > > The primary
>  EnergyPlus web site is found at: > http://www.energyplus.gov > > The
>  group web site is: >
>  http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are
>  not allowed -- please post any files to the > appropriate folder in
>  the Files are of the Support Web Site. > > > > > > > Your use of
>  Yahoo! Groups is subject to > http://docs.yahoo.com/info/terms/ > 
> 
> 
> 
>  ========================================================
>  Michael J. Witte, GARD Analytics, Inc.
>  EnergyPlus Testing and Support      
>  EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> Yahoo! Groups Sponsor	
> ADVERTISEMENT
> click here
> <http://rd.yahoo.com/M=251812.3170658.4537139.1261774/D=egroupweb/S=17
> 05007389:HM/A=1693352/R=0/SIG=11tralmvc/*http://www.netflix.com/Defaul
> t?mqso=60178293&partid=3170658> 	
>  <http://us.adserver.yahoo.com/l?M=251812.3170658.4537139.1261774/D=eg
>  roupmail/S=:HM/A=1693352/rand=279326846> 	
> 
>  To unsubscribe from this group, send an email to:
>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>  The primary EnergyPlus web site is found at:
>  http://www.energyplus.gov
> 
>  The group web site is:
>  http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>  Attachments are not allowed -- please post any files to the
>  appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
>  Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
>  <http://docs.yahoo.com/info/terms/> . 
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Upgrade to 128-Bit SSL Security!
> http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/