Hello,
From the EPlus source code is the definition of
DeltaTemp. TempCondInDesign & TempEvapOutDesign are entered by the User.
!Calculate chiller performance from this set of performance equations.
! from BLAST...Z=(TECONDW-ADJTC(1))/ADJTC(2)-(TLCHLRW-ADJTC(3))
!
DeltaTemp= (TempCondIn - TempCondInDesign) / TempRiseRat &
- (TempEvapOut - TempEvapOutDesign)
! from BLAST...RCAV=RCAVC(1)+RCAVC(2)*Z+RCAVC(3)*Z**2
!
AvailNomCapRat = CapacityRat(1) + CapacityRat(2) * DeltaTemp &
+ CapacityRat(3) * DeltaTemp ** 2
Thanks Richard Liesen
At 04:04 AM 9/26/2003, leeslwong wrote:
>Dear all,
>
>What is the equation to determine the delta T in the equation of
>Capacity Ratio Curve in Chiller:Electric?
>
>lee
>
>
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/