If you are reporting hourly, you are getting an average result over 
several HVAC timesteps.  Report results at the "detailed" frequency 
so that you can see data for every HVAC time step.  This may help 
explain what is happening.  

Mike


On 12 Oct 2003, at 16:26, Peter G Loutzenhiser wrote:

> All,
> I have built a simulation and when I run it I get both zone sensible
> heating and cooling rates during the same hours.  I am using Normal
> Damper Heating Action, but when I look at my zone output, I have mass
> flow rates above the minimum specified fraction.  I then look at my
> "Total water heating coil rate" I am still transferring heat into the
> air stream, which seems very odd.  Has anyone run into to similar
> problems, and is there a remedy?  Thanks.
> 
> 
> 
> Best Regards,
> 
> Peter Loutzenhiser
> post@xxxxxxxxxxx
> PhD Student
> Mechanical Engineering
> Iowa State University
> Office: 515-294-0365 
> 
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for your
> HP, Epson, Canon or Lexmark Printer at MyInks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs from home.
Over 14,500 titles. Free Shipping
& No Late Fees. Try Netflix for FREE!
http://us.click.yahoo.com/ArdFIC/hP.FAA/3jkFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/