Re: [EnergyPlus_Support] RE: Slab.exe
My apologies for the delayed response. You are correct. There
should be no extra layer of earth in the slab floor construction.
The slab program is reporting the temperature of the ground which is
in contact with the outside surface of the floor slab.
Mike
On 18 Oct 2003, at 19:05, Samuel Roose wrote:
> When using the slab program outlined in Lecture 24 of the EnergyPlus
> teaching materials, am I right in thinking that a layer of earth need
> not be placed in the floor construction once ground / outside face
> temperatures are found this way? For past models, I have used 1m of
> earth as part of the floor construction though I have never been too
> sure that this is particularly realistic. Sam Roose Victoria
> University of Wellington
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Rent DVDs from home. Over 14,500 titles.
> Free Shipping & No Late Fees. Try Netflix for FREE!
> http://us.click.yahoo.com/mk9osC/hP.FAA/3jkFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs from home.
Over 14,500 titles. Free Shipping
& No Late Fees. Try Netflix for FREE!
http://us.click.yahoo.com/mk9osC/hP.FAA/3jkFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/