My apologies for the delayed response.  After a quick look, I believe 
the problem is with the SET POINT MANAGER:OUTSIDE AIR object.  What 
you really want here is SET POINT MANAGER:MIXED AIR.  Refer to the 
5ZoneAuto example file for an example.  

Mike


On 14 Oct 2003, at 16:14, larry zhou wrote:

> Hello, everyone:
> 
> I am trying to build a Dual Duct VAV System in
> Energy-Plus. What I do is to modify the example idf
> file in the E+ example directory and add an
> economizer. Unfortunately, the economizer doesn?t
> work. I have been blocked by this issue for more
> than one week. Does anyone have some idea to solve
> the problem? Thanks a lot.
> 
> The attached text file is part of my E+ system model.
> Please let me know if you need more information or
> the complete idf file.
> 
> Lei Zhou
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Rent DVDs Online - Over 14,500 titles.
No Late Fees & Free Shipping.
Try Netflix for FREE!
http://us.click.yahoo.com/Tq9otC/XP.FAA/3jkFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/