RE: [EnergyPlus_Support] Zone mean air temperature



Thanks Mike, will try that.
Sam

	-----Original Message----- 
	From: Michael J. Witte [mailto:mjwitte@xxxxxxxx] 
	Sent: Sat 10/25/2003 4:21 AM 
	To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
	Cc: 
	Subject: RE: [EnergyPlus_Support] Zone mean air temperature
	
	
	Sam:
	
	That is puzzling.  The hot water and chilled water loops should 
	function independently.  The only place where they might interact 
	would be as each affects the space temperature.
	
	I see now that you have the two boilers in series with both active.  
	That was the main source of the problem.  When I put them in parallel 
	the max iteration warnings go away (all but one, which is acceptable, 
	probably during the warmup days).  Sorry I didn't notice this 
	earlier.  I will need to consult someone on the proper way to specify 
	boilers in series.
	
	Mike
	
	
	On 24 Oct 2003, at 23:59, Samuel Roose wrote:
	
	> Everything is now running to the heating set point, thanks Mike. You
	> were right to be suspicious of the boilers. When the boiler branch
	> control type is changed from "active" to "passive", the boilers all of
	> a sudden start working, and register readings. The trouble is, the
	> chillers no longer register as much load as they did before the boiler
	> change. These are currently set on active. I have tried iterations of
	> passive and active control. Seems I can get either boilers and
	> chillers working as they should, and either temperature or humidity
	> working as it should, but not all 4 parts working at once. My research
	> paper is due in five days so I am wrapping up my findings for now. I
	> am sure eventually the model will sort itself out. Thank you very much
	> for all your assistance.
	> 
	> Sam Roose
	> Victoria University of Wellington 
	> 
	>  -----Original Message----- 
	>  From: Michael J. Witte [mailto:mjwitte@xxxxxxxx] 
	>  Sent: Fri 24/10/2003 7:02 a.m. 
	>  To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
	>  Cc: 
	>  Subject: RE: [EnergyPlus_Support] Zone mean air temperature
	> 
	> 
	>  Sam:
	> 
	>  Did some more with this.  Main air loop had multiple supply and 
	>  return fans in series and many max iteration errors.  Tried changing 
	>  this to a single supply and return fan, did not help.  Noticed that 
	>  the heating load range was being exceeded and increased the upper 
	>  limit by a factor of 100 or so.  This helped, but there are still 
	>  many max iteration errors.  Added reporting of the plant loop outlet 
	>  temperature and boiler operation.  The plant loop temperature is 
	>  fluctuating widely and the boilers are never operating.  That's all 
	>  for today.    I suspect there is a problem with the hot water loop 
	>  and how it is connected or controlled.
	> 
	>  Mike
	> 
	> 
	>  On 8 Oct 2003, at 21:06, Samuel Roose wrote:
	> 
	>  > Mike,
	>  > I have just run the file for all 8760 hours of the year. What I am
	>  in > fact getting is temperature convergence to my heating set-point
	>  for > the first month of every simulation (the hourly temepratures
	>  were > obtained from one simulated month) then the temperatures all
	>  of a > sudden disregard the setpoints. It seems the heating system
	>  "runs out" > by February though I am not sure why. I have enclosed a
	>  graph in the > "Sam Roose" folder to demonstrate this problem. Thanks
	>  again, Sam > Roose Victoria University of Wellington > > 
	>  -----Original Message----- >  From: Michael J. Witte
	>  [mailto:mjwitte@xxxxxxxx] >  Sent: Wed 8/10/2003 4:59 a.m. >  To:
	>  EnergyPlus_Support@xxxxxxxxxxxxxxx >  Cc: >  Subject: Re:
	>  [EnergyPlus_Support] Zone mean air temperature > > >  When I try the
	>  same thing the average of the hourly values matches >  the monthly
	>  value.  Do you perhaps have a schedule on the monthly >  value which
	>  is suppressing certain hours of the day?  If not, please >  send your
	>  files so I can reproduce the problem.  > >  Mike > > >  On 7 Oct
	>  2003, at 18:22, Samuel Roose wrote: > >  > I have just simualted a
	>  file asking for a) the average internal >  > temperature in a zone
	>  per month and b) the hourly temperatures for >  the > same zone and
	>  month (July). When the hour by hour readings are >  > averaged, the
	>  average temperature result is very different (the > >  average is
	>  14.7 deg C for month by month and 19.3 deg C for hour by > >  hour.
	>  The building I am simulating is controlled to between 21 and 22 >  >
	>  deg C. This suggests to me that the calculation for average monthly >
	>   > temperature is incorrect, or that I am somehow misinterpreting my
	>  > >  output.  Any ideas? Thanks in advance, > > Sam Roose > Victoria
	>  >  University of Wellington > > ------------------------ Yahoo!
	>  Groups >  Sponsor > ---------------------~--> Buy Ink Cartridges or
	>  Refill Kits >  for your > HP, Epson, Canon or Lexmark Printer at
	>  MyInks.com. Free >  s/h on orders > $50 or more to the US & Canada. >
	>  >  http://www.c1tracking.com/l.asp?cid=5511 > > 
	>  http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM > > 
	>  ---------------------------------------------------------------------
	>  >  ~ > -> > > To unsubscribe from this group, send an email to: > > 
	>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx > > The primary > 
	>  EnergyPlus web site is found at: > http://www.energyplus.gov > > The
	>  >  group web site is: > > 
	>  http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are
	>  >  not allowed -- please post any files to the > appropriate folder
	>  in >  the Files are of the Support Web Site. > > > > > > > Your use
	>  of >  Yahoo! Groups is subject to > http://docs.yahoo.com/info/terms/
	>  > > > > >  ======================================================== >
	>   Michael J. Witte, GARD Analytics, Inc. >  EnergyPlus Testing and
	>  Support      >  EnergyPlus-Support@xxxxxxxx > > > > Yahoo! Groups
	>  Sponsor      > 
	>  <http://rd.yahoo.com/M=259395.3614674.4902533.1261774/D=egroupweb/S=1
	>  > 
	>  705007389:HM/A=1524963/R=0/SIG=12o885gmo/*http://hits.411web.com/cgi-
	>  >  bin/autoredir?camp=556&lineid=3614674&prop=egroupweb&pos=HM>      
	>  > 
	>  <http://us.adserver.yahoo.com/l?M=259395.3614674.4902533.1261774/D=eg
	>  >  roupmail/S=:HM/A=1524963/rand=695909087>       > >  To unsubscribe
	>  from this group, send an email to: > 
	>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx > >  The primary
	>  EnergyPlus web site is found at: >  http://www.energyplus.gov > > 
	>  The group web site is: > 
	>  http://groups.yahoo.com/group/EnergyPlus_Support/ > >  Attachments
	>  are not allowed -- please post any files to the >  appropriate folder
	>  in the Files are of the Support Web Site. > > > > > > >  Your use of
	>  Yahoo! Groups is subject to the Yahoo! Terms of Service > 
	>  <http://docs.yahoo.com/info/terms/> . > > > >
	>  ------------------------ Yahoo! Groups Sponsor >
	>  ---------------------~--> Buy Ink Cartridges or Refill Kits for your
	>  > HP, Epson, Canon or Lexmark Printer at MyInks.com. Free s/h on
	>  orders > $50 or more to the US & Canada. >
	>  http://www.c1tracking.com/l.asp?cid=5511 >
	>  http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM >
	>  ---------------------------------------------------------------------
	>  ~ > -> > > To unsubscribe from this group, send an email to: >
	>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx > > The primary
	>  EnergyPlus web site is found at: > http://www.energyplus.gov > > The
	>  group web site is: >
	>  http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are
	>  not allowed -- please post any files to the > appropriate folder in
	>  the Files are of the Support Web Site. > > > > > > > Your use of
	>  Yahoo! Groups is subject to > http://docs.yahoo.com/info/terms/ > 
	> 
	> 
	> 
	> Yahoo! Groups Sponsor      
	> ADVERTISEMENT
	> click here
	> <http://rd.yahoo.com/M=194081.4074964.5287182.1261774/D=egroupweb/S=17
	> 05007389:HM/A=1706996/R=0/SIG=11p5b9ris/*http://www.ediets.com/start.c
	> fm?code=30509&media=atkins>       
	>  <http://us.adserver.yahoo.com/l?M=194081.4074964.5287182.1261774/D=eg
	>  roupmail/S=:HM/A=1706996/rand=219729378>       
	> 
	>  To unsubscribe from this group, send an email to:
	>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
	> 
	>  The primary EnergyPlus web site is found at:
	>  http://www.energyplus.gov
	> 
	>  The group web site is:
	>  http://groups.yahoo.com/group/EnergyPlus_Support/
	> 
	>  Attachments are not allowed -- please post any files to the
	>  appropriate folder in the Files are of the Support Web Site.
	> 
	> 
	> 
	> 
	> 
	> 
	>  Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
	>  <http://docs.yahoo.com/info/terms/> . 
	> 
	> 
	> 
	> ------------------------ Yahoo! Groups Sponsor
	> ---------------------~--> Rent DVDs from home. Over 14,500 titles.
	> Free Shipping & No Late Fees. Try Netflix for FREE!
	> http://us.click.yahoo.com/mk9osC/hP.FAA/3jkFAA/dkFolB/TM
	> ---------------------------------------------------------------------~
	> ->
	> 
	> To unsubscribe from this group, send an email to:
	> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
	> 
	> The primary EnergyPlus web site is found at:
	> http://www.energyplus.gov
	> 
	> The group web site is:
	> http://groups.yahoo.com/group/EnergyPlus_Support/
	> 
	> Attachments are not allowed -- please post any files to the
	> appropriate folder in the Files are of the Support Web Site.
	> 
	> 
	> 
	> 
	> 
	> 
	> Your use of Yahoo! Groups is subject to
	> http://docs.yahoo.com/info/terms/ 
	> 
	
	
	
Yahoo! Groups Sponsor	
ADVERTISEMENT
click here <http://rd.yahoo.com/M=194081.4074964.5287182.1261774/D=egroupweb/S=1705007389:HM/A=1706996/R=0/SIG=11p5b9ris/*http://www.ediets.com/start.cfm?code=30509&media=atkins> 	
 <http://us.adserver.yahoo.com/l?M=194081.4074964.5287182.1261774/D=egroupmail/S=:HM/A=1706996/rand=714616362> 	

	To unsubscribe from this group, send an email to:
	EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
	
	The primary EnergyPlus web site is found at:
	http://www.energyplus.gov
	
	The group web site is:
	http://groups.yahoo.com/group/EnergyPlus_Support/
	
	Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
	
	
	
	
	
	
	Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 
	


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/