[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: Fw: [EnergyPlus_Support] Run a lot of input files (attached files embedded)



Joe,

How to modify it to run input files or weather files repetitively?

lee

At 01:23 PM 11/18/2003 -0800, you wrote:
>I guess EnergyPlus_Support does not accept attached files, so I've attached
>them manually to the end of this e-mail.
>
>Joe
>----- Original Message -----
>From: "Joe Huang" <YJHuang@xxxxxxx>
>To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
>Sent: Tuesday, November 18, 2003 1:19 PM
>Subject: Re: [EnergyPlus_Support] Run a lot of input files
>
>
> > I have written some simple batch procedures to run EnergyPlus repetitively
> > using a two-step process that utilizes EPMacro to preprocess a master
>input
> > file containing macros.
> >
> > (1) doepall.bat passes to runepmacro.bat the arguments for the macro
> > definitions for each simulation.
> >
> > (2) runepmacro.bat echos the macro arguments as ##set1's to the in.imf,
>and
> > then adds the master input file (here called
>LgOff_t24_baselineSATR13e.imf)
> > containing macros. This file is then run through epmacro and then through
> > EnergyPlus itself.  There are some postprocessing procedures afterwards
> > using the "awk"  programming language, but those are incidental to the
>whole
> > procedure.
> >
> > Both doeplus.bat and runepmacro.bat are attached.
> >
> > Joe Huang
> >
> > ----- Original Message -----
> > From: "leeslwong" <bclwong@xxxxxxxxxxxx>
> > To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
> > Sent: Monday, November 17, 2003 10:16 PM
> > Subject: [EnergyPlus_Support] Run a lot of input files
> >
> >
> > > Dears,
> > >
> > > I wonder if someone can give me an example file of runeplus.bat for
> > > running a lot of numbers of input files for e+ simulation at the same
> > > time? And what is the procedures to use it and run it?
> > >
> > > Thanks
> > >
> > > lee
> > >
>
>doepall.bat
>-------------
>rem                 lec evap ctz systm
>rem                 typ  ach wth contrl peop lites eqp
>rem --------------------------------------------
>rem ----- CTZ04 Sunnyvale
>     call runEPmacro VAV    0  04  cool  t24  t24  t24
>rem call runEPmacro VAV    0  04 none none none
>rem call runEPmacro Evap1  4  04  cool  t24  t24  t24
>rem call runEPmacro Evap1  8  04  cool  t24  t24  t24
>rem call runEPmacro Evap1 12  04  cool  t24  t24  t24
>rem call runEPmacro Evap2  4  04  cool  t24  t24  t24
>rem call runEPmacro Evap2  8  04  cool  t24  t24  t24
>rem call runEPmacro Evap2 12  04  cool  t24  t24  t24
>rem ----- CTZ07 San Diego
>rem call runEPmacro VAV    0  07  cool  t24  t24  t24
>rem call runEPmacro Evap1  4  07  cool  t24  t24  t24
>rem call runEPmacro Evap1  8  07  cool  t24  t24  t24
>rem call runEPmacro Evap1 12  07  cool  t24  t24  t24
>rem call runEPmacro Evap2  4  07  cool  t24  t24  t24
>rem call runEPmacro Evap2  8  07  cool  t24  t24  t24
>rem call runEPmacro Evap2 12  07  cool  t24  t24  t24
>rem ----- CTZ09 Pasadena
>rem call runEPmacro VAV    0  09  cool  t24  t24  t24
>rem call runEPmacro Evap1  4  09  cool  t24  t24  t24
>rem call runEPmacro Evap1  8  09  cool  t24  t24  t24
>rem call runEPmacro Evap1 12  09  cool  t24  t24  t24
>rem call runEPmacro Evap2  4  09  cool  t24  t24  t24
>rem call runEPmacro Evap2  8  09  cool  t24  t24  t24
>rem call runEPmacro Evap2 12  09  cool  t24  t24  t24
>rem ----- CTZ12 Sacramento
>rem call runEPmacro VAV    0  12  cool  t24  t24  t24
>rem call runEPmacro Evap1  4  12  cool  t24  t24  t24
>rem call runEPmacro Evap1  8  12  cool  t24  t24  t24
>rem call runEPmacro Evap1 12  12  cool  t24  t24  t24
>rem call runEPmacro Evap2  4  12  cool  t24  t24  t24
>rem call runEPmacro Evap2  8  12  cool  t24  t24  t24
>rem call runEPmacro Evap2 12  12  cool  t24  t24  t24
>
>runEPMacro.bat
>------------------
>echo !- ******* begin of "macro&runcontrol.inc" include file ****** > in.imf
>echo !-  ======= LEC Parametric variables ====== >> in.imf
>echo !- For now, lets put all the parametric run variable in this top
>section >> in.imf
>echo ##set1 lec_systems %1 >> in.imf
>echo ##set1 evap_ach %2 >> in.imf
>echo ##set1 location %3 >> in.imf
>echo ##set1 cooling %4 >> in.imf
>echo ##set1 people %5 >> in.imf
>echo ##set1 lights %6 >> in.imf
>echo ##set1 equip %7 >> in.imf
>copy in.imf + LgOff_t24_baselineSATR13.imf in.imf
>c:\EnergyPlus\EP-Macro\EPMacro
>rem
>rem  clean up from EP-Macro
>rem
>rem pause
>erase in.imf
>erase audit.out
>copy out.idf %1.%2ach.ctz%3.idf
>copy out.idf in.idf
>erase out.idf
>rem
>echo ===== running EnergyPlus with LgOff_t24_baselineSATR13 with %1 and
>ctz%3c weather =====
>copy c:\EnergyPlus_Working\DATA\"Energy+03_0911.idd"  "Energy+.idd"
>pkunzip c:\Energy~3\WEATHER\ctz%3c.zip
>rem
>move ctz%3cDO.epw in.epw
>rem
>c:\EnergyPlus_Working\Executables\EnergyPlus03_0911
>rem
>c:\EnergyPlus\Release\PostProcess\ReadVarsESO
>awk -f UTIL\readhrly.awk eplusout.csv > OUTPUTS\%1.%2ach.ctz%3.hrl
>erase HEAD.1
>erase HEAD.2
>rem
>move audit.out OUTPUTS\%1.%2ach.ctz%3.audit
>move eplusout.err OUTPUTS\%1.%2ach.ctz%3.err
>move eplusout.end OUTPUTS\%1.%2ach.ctz%3.end
>move eplusout.eio OUTPUTS\%1.%2ach.ctz%3.eio
>move eplusout.eso OUTPUTS\%1.%2ach.ctz%3.eso
>move eplusout.bnd OUTPUTS\%1.%2ach.ctz%3.bnd
>move eplusout.mtd OUTPUTS\%1.%2ach.ctz%3.mtd
>move eplusout.mtr OUTPUTS\%1.%2ach.ctz%3.mtr
>move eplusout.dxf OUTPUTS\%1.%2ach.ctz%3.dxf
>move eplusout.audit OUTPUTS\%1.%2ach.ctz%3.audit
>move eplusout.zsz OUTPUTS\%1.%2ach.ctz%3.zsx
>move eplusout.rdd OUTPUTS\%1.%2ach.ctz%3.rdd
>move eplusout.ssz OUTPUTS\%1.%2ach.ctz%3.ssz
>move eplusout.csv OUTPUTS\%1.%2ach.ctz%3.csv
>move eplusout.cif OUTPUTS\%1.%2ach.ctz%3.cif
>erase eplusout.dbg
>del in.idf >nul
>del in.epw >nul
>del "Energy+.idd" >nul
>del "Energy+.ini" >nul
>echo ===== EnergyPlus with LgOff_t24_baselineSATR13 with %1 and ctz%3c
>weather completed =====
>:end
>
>
>Yahoo! Groups Sponsor
>ADVERTISEMENT
><http://rd.yahoo.com/SIG=12cqdnl9i/M=267637.4116730.5333196.1261774/D=egroupweb/S=1705007389:HM/EXP=1069276937/A=1853618/R=0/*http://www.netflix.com/Default?mqso=60178338&partid=4116730>5121bf.jpg
>5121f1.jpg
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
><http://www.energyplus.gov>http://www.energyplus.gov
>
>The group web site is:
><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to the 
><http://docs.yahoo.com/info/terms/>Yahoo! Terms of Service.

  ----------



[Non-text portions of this message have been removed]


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/