Re: [EnergyPlus_Support] Average COP of chillers



I am using 1.1.0.020.

lee

At 12:10 PM 11/24/2003 -0600, you wrote:
>Are you using 1.1.0.018 or 1.1.0.020?  There was a significant bug in 
>1.1.0.018
>related to chiller part load power consumption which was fixed for the
>1.1.0.020 release.
>
>Mike
>
>
>On 24 Nov 2003, at 15:22, leeslwong wrote:
>
> > I used the E+ version 1.1.0 to simulate my reference building with
> > six identical electric air-cooled chillers. The cooling capacity of
> > each chiller is 1060kw and the nominal COP is 2.8. The used part load
> > curves are follow the example file of the E+ program. After
> > simulation, the total annual cooling demand (chiller loop demand) is
> > 9196MWh and the total annual chillers' electricity consumption is
> > 8.8x10^2 J (2144MWh). The calculated average COP is about 3.76. The
> > question is why the calculated COP of 3.76 is extremely higher the
> > nominal COP I enter into the input file? Is it anything wrong in my
> > input file or anything wrong in version 1.1.0 of E+? Is result will
> > be more reasonable if using the version 1.1.1 of E+? Please give me
> > advices.
> >
> > Thanks
> >
> > lee
> >
> >
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > <http://www.energyplus.gov>http://www.energyplus.gov
> >
> > The group web site is:
> > 
> <http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate 
> folder
> > in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to 
> <http://docs.yahoo.com/info/terms/>http://docs.yahoo.com/info/terms/
> >
>
>
>
>========================================================
>Michael J. Witte, GARD Analytics, Inc.
>EnergyPlus Testing and Support
>EnergyPlus-Support@xxxxxxxx
>
>
>Yahoo! Groups Sponsor
>ADVERTISEMENT
><http://rd.yahoo.com/SIG=12c26t9p4/M=267637.4116732.5333197.1261774/D=egroupweb/S=1705007389:HM/EXP=1069785408/A=1853619/R=0/*http://www.netflix.com/Default?mqso=60178356&partid=4116732>7f471.jpg
>7f4e9.jpg
>
>To unsubscribe from this group, send an email to:
>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>The primary EnergyPlus web site is found at:
><http://www.energyplus.gov>http://www.energyplus.gov
>
>The group web site is:
><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate 
>folder in the Files are of the Support Web Site.
>
>
>
>
>
>
>Your use of Yahoo! Groups is subject to the 
><http://docs.yahoo.com/info/terms/>Yahoo! Terms of Service.

  ----------



[Non-text portions of this message have been removed]


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/