Re: [EnergyPlus_Support] Crashed file for illuminance map generation



There is an error in the zone pointers used to grab the reference point 
coordinates which are included in the illuminance map output.  These reference 
point coordinates will only be correct if the ZONE object list is parallel to 
the DAYLIGHTING:DETAILED object list.  Note that these coordinates are only 
listed for reference and do not impact the values in the illuminance map.

In your case, the bad pointers lead to an array subscript error.  To fix this 
problem, change the order of your ZONE objects to match the order of your 
DAYLIGHTING:DETAILED objects.  In your file, the first ZONE object should be 
GFSP-N, then GFSP-E, GFSP-S, GFSP-W which is what you have.  But then the next 
ZONE objects should be SP-N, SP-E, SP-S, SP-W, RFSP-N, RFSP-E, RFSP-S, RFSP-W.

Mike


On 3 Dec 2003, at 10:23, leeslwong wrote:

> I've just uploaded a input file (new.idf) for daylighting simulation 
> for a 3-storey building. I add the "illuminance map" function into my 
> file. After running, it crashed. I wonder if anyone can tell me what 
> the problem is and how it can be fixed.
> 
> Thanks
> 
> lee
> 
> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/ 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/