Re: [EnergyPlus_Support] Re: COMSI AIR FLOW:OPENING=>Discharge coefficient ?
Ming,
My responses follow.
Joe
----- Original Message -----
From: "waspoorboy" <mingsbox@xxxxxxxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, December 08, 2003 10:53 PM
Subject: [EnergyPlus_Support] Re: COMSI AIR FLOW:OPENING=>Discharge
coefficient ?
> Joe,
>
> Thanks for your explanation.
>
> For crack, Q=Cp*(delta P)^n
>
> For opening, Q= Cd*A* f(delta P)
>
> 1.The airflow calculation for LVO is some complicated function in
> COMIS, much more complicated than crack flow. (Y/N)
Yes.
> 2.The calculation algorithm of LVO is not explained in COMIS 3.0 user
> guide, is there any manuals or publications that talk about it ?
The mathematics is explained in COMIS Fundamentals, edited by H. Feustel and
A. Rayner-Hooson, LBL-28560, Lawrence Berkeley Laboratory, May 1990. I've
scanned in and attached a few pages describing the solution for air flow
through large openings. Please contact Brian Smith at BVSmith@xxxxxxx if you
want a copy of COMIS Fundamentals.
>
> 3.If Cd is specified by user (not zero), then COMIS will use it and
> not determine the Cd from the other input parameters. (Y/N)
Yes.
> 4.For EnergyPlus/COMIS to determine Cd itself, the user specify all
> Cd to zero for all opening factors. (I mean does this work in
> EnergyPlus/COMIS as in COMIS 3.0) (Y/N)
Yes.
> 5.Is it recommended to let COMIS determine Cd itself ? (Y/N)
Yes, unless you have a good value for Cd.
> 6.E+ I/O ref manual p.245 says Cd should be 0.0 ~ 1.0,
> but COMIS 3.0 manual p.62 says Cd can be up to ~ 1.5,
> does it work in E+ when Cd > 1.0 ? (Y/N)
Yes, I think so, although I haven't verified that.
>
> 7.COMIS AIR FLOW:Opening,
> W_Window, !- Name
> .0001, !- Air Mass Flow Coeff Window or Door Is Closed
>
> some combinations of Air Mass Flow Coeff cause error message
> in E+/COMIS:
> **Fatal** Error in the ventilation part! MATRIX SINGULAR FOR ZONE #6
> Is there any solutions ?
>
> Thanks again,
> Ming
>
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
>
>
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/