Re: [EnergyPlus_Support] Crashed file for illuminance map generation
This run ultimately crashed with the same problem that your smaller file had.
The order for the ZONE objects and the DAYLIGHTING:DETAILED objects must be the
same to avoid the pointer bug in the illuminance map module. If I understand
your structure correctly, then all of the ZONE objects for the *-I and *CORE
zones must come after all of the other zones.
Mike
On 12 Dec 2003, at 15:30, Michael J. Witte wrote:
> Lee:
>
> When I first ran this on my machine it crashed due to "insufficient virtual
> memory". Please run this file in ep-launch with "View-->Pause During
> Simulation" selected and confirm if you receive a similar error message.
>
> If so, this means that you need to increase the size of your virtual memory page
> file. In Windows 2000, the procedure is as follow:
>
> Go to the control panel (Start --> Settings --> Control Panel)
> Open the System control panel
> Select the Advanced tab
> Select Performance Options
> Under Virtual Memory select Change
>
> In this dialog, you can set the sizes for paging files on each hard drive. Your
> file is now running on my machine. With some other applications open, the Task
> Manager (right-click the toolbar and open task manager) says I'm using nearly
> 1.4 GB of memory. The big jump in memory came when the message "Calculating
> Daylighting Factors" showed in the EnergyPlus window. It's been at that point
> for over an hour now. You'll need to set your total paging file maximum size
> plus physical RAM to be greater than 1.4 GB in order for this to run.
>
> Mike
>
>
>
>
> On 10 Dec 2003, at 15:04, Wong, S L wrote:
>
> > Mike,
> >
> > The problem has been fixed. After that I've simulated a 40-storey building.
> > Each floor consists of four parameter zones which are the North, East, South
> > and West, so total no. of zones with daylighting control are 160. I followed
> > your instructions to generate illuminance maps of these zones and the run
> > period is from 1/1 to 12/31 hourly. After simulation, the file was crashed
> > again. Is it any limitation of E+ in generating illuminance maps (i.e. nos of
> > zones, nos. of day, etc.)? How can I fix it again?
> >
> > Thanks
> >
> > lee
> >
> > At 11:51 AM 12/3/2003 -0600, you wrote:
> > >There is an error in the zone pointers used to grab the reference point
> > >coordinates which are included in the illuminance map output. These
> > >reference
> > >point coordinates will only be correct if the ZONE object list is parallel to
> > >the DAYLIGHTING:DETAILED object list. Note that these coordinates are only
> > >listed for reference and do not impact the values in the illuminance map.
> > >
> > >In your case, the bad pointers lead to an array subscript error. To fix this
> > >problem, change the order of your ZONE objects to match the order of your
> > >DAYLIGHTING:DETAILED objects. In your file, the first ZONE object should be
> > >GFSP-N, then GFSP-E, GFSP-S, GFSP-W which is what you have. But then the
> > >next ZONE objects should be SP-N, SP-E, SP-S, SP-W, RFSP-N, RFSP-E, RFSP-S,
> > >RFSP-W.
> > >
> > >Mike
> > >
> > >
> > >On 3 Dec 2003, at 10:23, leeslwong wrote:
> > >
> > > > I've just uploaded a input file (new.idf) for daylighting simulation
> > > > for a 3-storey building. I add the "illuminance map" function into my
> > > > file. After running, it crashed. I wonder if anyone can tell me what the
> > > > problem is and how it can be fixed.
> > > >
> > > > Thanks
> > > >
> > > > lee
> > > >
> > > >
> > > >
> > > > To unsubscribe from this group, send an email to:
> > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > >
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > >
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >
> > > > Attachments are not allowed -- please post any files to the appropriate
> > > folder
> > > > in the Files are of the Support Web Site.
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> > > >
> > >
> > >
> > >
> > >========================================================
> > >Michael J. Witte, GARD Analytics, Inc.
> > >EnergyPlus Testing and Support
> > >EnergyPlus-Support@xxxxxxxx
> > >
> > >
> > >
> > >To unsubscribe from this group, send an email to:
> > >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > >The primary EnergyPlus web site is found at:
> > >http://www.energyplus.gov
> > >
> > >The group web site is:
> > >http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > >Attachments are not allowed -- please post any files to the appropriate
> > >folder in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > >
> > >Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> >
> >
> >
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/