You can create subhourly schedules using DAYSCHEDULE:INTERVAL and 
DAYSCHEDULE:LIST.  Then use these schedules in your PLANT OPERATION SCHEMES 
object.

Note that all schedules are resolved to the zone time step.  For example, if 
you set TIMESTEP IN HOUR = 4, the zone time step will be 15 minutes.  If you 
describe a subhourly schedule with 10-minute intervals, the schedule values 
will be interpolated to determine the value every 15 minutes to match the zone 
time step.

Mike



On 5 Jan 2004, at 5:08, Helen Xing wrote:

> Hello,
> 
> Wonder if it is possible to turn chiller off for less than an hour in E+ 
> simulation.  Apparently not doable if one defines the relevant schedules on a
> 24-hour basis.  Thanks for your help!
> 
> 
> Helen Xing
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
>  -- please post any files to the appropriate folder in the Files are of the
>  Support Web Site.
> 
> 
> 
> 
> 
> 
> Yahoo! Groups Links
> 
> To visit your group on the web, go to:
>  http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> To unsubscribe from this group, send an email to:
>  EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> Your use of Yahoo! Groups is subject to:
>  http://docs.yahoo.com/info/terms/ 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-bit SSL Security!
http://us.click.yahoo.com/qZ0LdD/yjVHAA/TtwFAA/dkFolB/TM
---------------------------------------------------------------------~->

Yahoo! Groups Links

To visit your group on the web, go to:
 http://groups.yahoo.com/group/EnergyPlus_Support/

To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

Your use of Yahoo! Groups is subject to:
 http://docs.yahoo.com/info/terms/