[EnergyPlus_Support] Supply air temperature control
Hi
I am having problems with my program not keeping the supply air temperature
at the appropriate setpoint. I have used purchase chilled water and have
more than enough capacity. My cooling coil has water supplied at 3°C
and a delta T of 9°C. The supply air temperature is set at 12°C. The
trend I have been seeing is that when the cooling coil has the maximum flow
rate of water through it, it can not meet the supply air
setpoint. However, when the max flow rate is present, the temperature rise
of the water is only 1-2°C. When the setpoint is actually met, the flow
rate through the coil is usually small and the temperature rise of the
water is often large. Many times the temperature rise is about 12-15°C
which is more than the design value of 9°C. Also, there seems to be a
large gap in flow rates between the maximum and the flow rates at the times
where the setpoint temperature is met. My cooling coil UA is about 2000
W/delK which has been on autosize. I have tried to increase the UA
manually and this has not solved the problem. I have also adjusted the
chilled water capacity with no luck. The delta T of the cooling water has
also been adjusted. Any suggestions of what might be happening?
Mike McCarty
Graduate Student, Mechanical Engineering
Iowa State University
2043 Black Engineering
Ames, IA 50010
515-294-3080
mmccarty@xxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/