Hello,
Currently there are more than inlet node to a zone and its purpose was to
allow for multiple systems to serve the zone or for systems that required
more than 1 inlet node. So the simple answer is yes you can have more than
1 system serve a zone and then these multiple units are prioritized in the
Controlled Zone Configuration to let the program know which ones to use
first to meet the loads.
Thanks Richard Liesen
At 07:37 AM 2/19/2004, David Cormier wrote:
>hello,
>
>I have to model a shop that have 5 vav system with no rehaeat (5 rooftop
>units) in the same area. Can I put the system in parallel (5 intel node
>with a big mixer at the outlet of the roof top unit) ??
>Or we can't put more then 1 unit per zone?? (In this case, I will need to
>construct virtual wall to separate the area in many zones ???)
>
>thank you
>
>David
>
>_________________________________________________________________
>MSN Messenger : discutez en direct avec vos amis !
>http://messenger.fr.msn.ca/
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files are of the Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder in the Files are of
> the Support Web Site.
>
>
>
>
>
>Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/