Re: [EnergyPlus_Support] warm-up time



				Yes, EnergyPlus simulates the first day of
each simulation period until it
				reaches 'convergence".  You will notice this
when, at the beginning of the 
				runs, it says 'warming up'.  

				You can set the maximum number of warmup
days in the Building object
				(see pgs. 34 and 37 of 807 in the I-O
reference).  You can also see the 
				number of warmup days used in the
eplusout.eio file  (Environment:WarmupDays, X).






	Mohit Mehta <mohitmehta1@xxxxxxxxx>
			03/11/2004 12:38 AM
			Please respond to EnergyPlus_Support
					
	To:	EnergyPlus_Support@xxxxxxxxxxxxxxx@SMTP@Exchange
	cc:	
	Subject:	[EnergyPlus_Support] warm-up time	



				hi:

				if am running a simulation of a high mass NV
building between aug 14 - 17 (4 hot days) - shouldn't the building take a
few hours or days to warm up? like indoor and outdoor temperatures starting
out the same on the first day (aug 14), and indoor air temperatures climbing
gradually over the four-day period; finally balancing out? it appears that
the mass starts out as preheated (warmed/cooled). does it use 3-4 warm-up
days before the days that i am looking at are reported?

				thank you. 

				~m


				---------------------------------
				Do you Yahoo!?
				Yahoo! Search - Find what you?re looking for
faster.

				[Non-text portions of this message have been
removed]



				The primary EnergyPlus web site is found at:
				http://www.energyplus.gov

				The group web site is:
	
http://groups.yahoo.com/group/EnergyPlus_Support/

				Attachments are not allowed -- please post
any files to the appropriate folder in the Files are of the Support Web
Site.




				 -- please post any files to the appropriate
folder in the Files are of the Support Web Site.




				 
				Yahoo! Groups Links

http://groups.yahoo.com/group/EnergyPlus_Support/

	
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

				 





[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/