Re: [EnergyPlus_Support] generating weather file
There are ways to generate approximate hourly data from limited weather
information. A study of weather records several years ago (Cash et al)
shows that temperatures can be estimated with about 10% accuracy using a
simple cyclodial function based on average temperature and daily
extremes. You could modify this a bit so that low temperatures occur
just before dawn.
Solar can be calculated from equations for your sire. The problem is
that we can reasonably calculate a clear day solar gain, but estimating
the effects of cloud cover is still a crap shoot.
Rain is not much of a problem because E+ uses just a rain indicator, not
a measured amount.
you need something for wind. Moisture (outside RH) is another matter.
I don't know of any studies that try to preict outdie dew point
temperature cycles.
Any wha, you have a lot of data to gather and put in a spreadsheet that
the weather generator coupd process.
Have you got enough time to record your own sit data?
Ned Lyon
Senior Project Manager
Simpson Gumpertz & Heger Inc.
41 Seyon Street
Building #1, Suite 500
Waltham, MA 02453
Phone: 781-907-9000
Fax: 781-907-9009
>>> teklay1979@xxxxxxxxx 03/13/04 3:38 AM >>>
Mike
last time i have comunicated with Drury Crawley from
DOE but he/she can't find the place that i need. so i
need to generate my self. so could you help me to work
this.
* can Energy Plus accept monthly data?
* what can i do if the data are not available ?
Tek
--- "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> What specific location(s) do you need data for?
>
> Mike
>
>
> On 11 Mar 2004, at 7:47, teklay Weldeabzgi wrote:
>
> >
> > I am trying to simulate new buildings. but here
> in my
> > country the national meteorological service
> doesn't
> > have enough weather data for the place i need. but
> > they have only monthly average, and i need to
> > interpolate and generate an .epw data to use in my
> > simulation.
> > So is there any one help me how can i do this.
> > please tell me the steps and procuders to follow
> or is
> > there any method to work on this
> >
> > Tek.
> >
> > __________________________________
> > Do you Yahoo!?
> > Yahoo! Search - Find what you're looking for
> faster
> > http://search.yahoo.com
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any
> files to the appropriate folder
> > in the Files are of the Support Web Site.
> >
> >
> >
> >
> > -- please post any files to the appropriate
> folder in the Files are of the
> > Support Web Site.
> >
> >
> >
> >
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
>
>
========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files
> to the appropriate folder in the Files are of the
> Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
>
>
>
>
>
> Yahoo! Groups Links
>
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
>
>
__________________________________
Do you Yahoo!?
Yahoo! Mail - More reliable, more storage, less spam
http://mail.yahoo.com
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of
the Support Web Site.
Yahoo! Groups Links
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/