Shouldn't the "Opaque Surface Inside Face Conduction" be equal to the amount of heat flux entering a zone combining the convection and radiation. I thought that using "SurfaceInsideTemperature - ZoneAir Temperature) * SurfaceArea * SurfaceInsideConvectionCoefficient" just accounted for the convective effect on the zone. I thought the heat flux infinitesimally inside the wall surface should be equal to the heat flux to or from the zone. Am I wrong in this assumption. Does the SurfaceInsideConvectionCoefficient incorporate the radiation and convective heat transfer.
Thanks
Ian
----- Original Message -----
From: Michael J. Witte
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, April 06, 2004 3:34 PM
Subject: Re: [EnergyPlus_Support] report
Opaque Surface Inside Face Conduction is intended for detailed examination of
the heat balance on a particular inside surface, primarly to support
comparisons with measured data. It is not meaningful as a component of the
current heating or cooling load. Surfaces interact with the zone air heat
balance by convection. So, the value of most interest is
(SurfaceInsideTemperature - ZoneAir Temperature) * SurfaceArea *
SurfaceInsideConvectionCoefficient to calculate the current load due to the
surfaces. This will include the current load due to solar gains, because solar
becomes a load by warming a surface.
For an example of comparing the load with a hand calculation, see files
UAdeltaT,zip and UAdeltaT2.zip in
http://groups.yahoo.com/group/EnergyPlus_Support/files/Examples/
Mike
On 5 Apr 2004, at 20:16, David Cormier wrote:
> Hello,
>
> I do a simple test with EnergyPlus. It's about a simple room with no
> internal load. I look at the result
>
> If I add : ZONE1:Zone Window Heat Gain[W](Hourly) + MUR1:Opaque Surface
> Inside Face Conduction Loss[W](Hourly) or gain for my wall + TOIT:Opaque
> Surface Inside Face Conduction Loss[W](Hourly) or gain
>
> I think that I suppose to have the same result as ZONE1:Zone/Sys Sensible
> Load Predicted[W](Hourly). In heating, its ok, but in cooling, I have a
> mistake because the result of the add is always higher than the result of
> ZONE1:Zone/Sys Sensible Load Predicted[W]
>
> I suppose that I forget a term in the add ... Do you have an idea?
>
> David Cormier
>
> _________________________________________________________________
> MSN Messenger : discutez en direct avec vos amis !
> http://messenger.fr.msn.ca/
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
>
>
>
>
> -- please post any files to the appropriate folder in the Files are of the
> Support Web Site.
>
>
>
>
>
> Yahoo! Groups Links
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
------------------------------------------------------------------------------
Yahoo! Groups Links
a.. To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
b.. To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
c.. Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
-- please post any files to the appropriate folder in the Files are of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/