Re: [EnergyPlus_Support] Condenser outlet temperature



For air and evap cooled chillers, the condenser outlet temperature is not 
calculated.  To calculate this temperature, you would need to determine the air 
flow rate through the condenser and then use the relationship 

Qcondenser [W] = AirVolumeFlowRate [m3/s] * Density [kg/m3] * SpecificHeat 
[J/kg-K] * (Tout - Tin) [K]

Mike


On 20 Apr 2004, at 21:26, HSIEH Chun-Ming wrote:

> Dear sirs:
> 
> For a water-cooled chiller,
> there is an ouput, Chiller Cond Water Outlet Temp, to report the outlet 
> temperature of a chiller.
> On the other hand, there is no such outlet temperature report for an 
> air-cooled chiller.
> The same situation in the case of a window air conditioner.
> 
> What I want to know is the exhaust air temperature that discharged from 
> a window air conditioner.
> Is there an output related to the oulet temperature?
> If no,
> which equation is available for me to calculate the outlet temperature 
> from the EnergyPlus output (heat rejection/heat transfer (J)).
> or what other else parameters/information (airflow rate, for example) we 
> need to calculate the oulet temperature.
> Heat and Temperature are always confusing me.
> Thank you very much.
> 
> Chunming
> 
> 
> 
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com.  Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/