RE: [EnergyPlus_Support] Orphan Object: Generator:PV:Simple



Stephen,
 
Thanks for sending me your input file.  Here is a summary of why it wasn't working. 
 
1 .  the file needed an ELECTRIC LOAD CENTER:DISTRIBUTION object
 
2.  Two fields in ELECTRIC LOAD CENTER:GENERATORS were missing.  One of these refers to an availability schedule, which also needed to be defined elsewhere in the file.  
 
3.  To use the building INTEGRATED PV mode you have to use the object CONSTRUCTION WITH INTERNAL SOURCE for that surface (rather than CONSTRUCTION).  The "source" is actually treated as sink to account for electrical energy exported from the surface.
 
4.  the surface named in the GENERATOR:PV:SIMPLE did not match the name in the Surface:HeatTransfer
 
I'll send you the new input file in a separate email
 
Brent
 
 

[Griffith, Brent] 
 -----Original Message-----
From: Michael J. Witte [mailto:mjwitte@xxxxxxxx]
Sent: Thursday, April 22, 2004 8:34 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Orphan Object: Generator:PV:Simple



Without seeing your file, I would guess that you need to add ELECTRIC LOAD 
CENTER:DISTRIBUTION and ELECTRIC LOAD CENTER:GENERATORS to your idf file.  See 
the GeneratorswithPV.idf example file.

Mike


On 22 Apr 2004, at 8:23, Linda Lawrie wrote:

> Sorry, Stephen.  Attachments are not allowed on the list.
> 
> Can you post your files to the web site/ files area (problems) or send them
> directly to me (linda@xxxxxxxxxx) or energyplus-support@xxxxxxxx
> 
> We'll take a look at them.
> 
> At 04:18 AM 4/22/2004, Stephen K Wittkopf wrote:
> >I am having the problem that the object is never 'gotten', as the
> >attached audit file puts it.
> 
> Linda
> 
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




  _____  

Yahoo! Groups Links


*	To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
  

*	To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
  

*	Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 




[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/