From the code:
! Determine Sky Temp ==>
! Function of DryBulb, DewPoint, OpaqueSkyCover
! Calculate Sky IR
!HIR = ESKY * SIGMA * (TOUT**4)
!
!where
!
!HIR = horizontal IR intensity (W/m2)
!ESKY = sky emissivity
!SIGMA = Stefan-Boltzmann constant = 5.6697e-8 W/m2-K4
!TOUT = drybulb temperature (K)
!
!The sky emissivity is given by
!
!ESKY = [0.787 + 0.764*ln(TDEW/273)]*[1 + 0.0224*N - 0.0035*(N**2)
+ 0.00028*(N**3)]
!
!where
!
!TDEW = dewpoint temperature (K)
!N = opaque sky cover (tenths)
!
!Example: Clear sky (N=0), TOUT = 273+20=293K, TDEW = 273+10=283K:
!
!ESKY = 0.787 + 0.764*0.036 = 0.815
!HIR = 0.815*5.6697e-8*(293**4) = 340.6 W/m^2
!References:
!
!George N. Walton, "Thermal Analysis Research Program Reference
Manual,"
!NBSIR 83-2655, March 1983, p. 21.
!
!G. Clark and C. Allen, "The Estimation of Atmospheric Radiation
for Clear and
!Cloudy Skies," Proc. 2nd National Passive Solar Conference
(AS/ISES), 1978, pp. 675-678.
(It would normally be in the Auxiliary programs document as we intend that
the epw files will have this information but it looks like it isn't there).
It may be a little dated -- someone proposed some different methods shortly
before the last release but were unable to lead us to a definitive
algorithm nor could we determine universiality.
At 03:32 AM 5/6/2004, g_kokogiannakis wrote:
>was looking the engineering reference for this but could not find
>something.
>I took the sky temperatures from the results in EnergyPlus and
>compared them with the predictions of some models from the literature
>(Cole's, Clarke's, Czeplak, e.t.c. - for the same weather file).
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
---------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/